EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:45 PM . Last Modified: 2024-04-04 02:47 AM
Hello!
From this page, and according to Steven Marchetti, "The data DCE gathers and stores is only that data polled using SNMP or modbus depending on the configuration".
I'd like to see how much data DCE has gathered and stored for each node. Is this possible?
At the moment, from the "Storage Settings", all I can see is the overall "Sensor Data, Logs, Database and Other" usage.
Any help, please?
Thanks
(CID:134026644)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:46 PM . Last Modified: 2024-04-04 02:47 AM
Hi Seun,
Sorry but there is no way to determine exactly how much memory is being used for each node monitored. It's easy enough to average this out as you may have say 50 devices and 25 gigs worth of sensor data. Each device would then be using an average of 1/2 gig.
Problem with that is one unit may have hundreds of sensors while another has just a few. Additionally you can set certain units to be polled at a different frequency than others so this average may not be totally accurate.
Under the "Resources" menu on top of this page, there is an option to add a feature request but I can't say that this is something that is requested a lot so I'm not sure it would actually make it into the current product.
Thanks,
Steve
(CID:134026653)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:46 PM . Last Modified: 2024-04-04 02:47 AM
Hi Seun,
Sorry but there is no way to determine exactly how much memory is being used for each node monitored. It's easy enough to average this out as you may have say 50 devices and 25 gigs worth of sensor data. Each device would then be using an average of 1/2 gig.
Problem with that is one unit may have hundreds of sensors while another has just a few. Additionally you can set certain units to be polled at a different frequency than others so this average may not be totally accurate.
Under the "Resources" menu on top of this page, there is an option to add a feature request but I can't say that this is something that is requested a lot so I'm not sure it would actually make it into the current product.
Thanks,
Steve
(CID:134026653)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:46 PM . Last Modified: 2024-04-04 02:46 AM
Alright. Thanks Steve
(CID:134026674)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 10:46 PM . Last Modified: 2023-10-22 02:23 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.