DCE has a function to allow an alarm tied to a rate of change in temperature.
So the function to look at a number and compare it to the number in 5 minutes exists. There is nothing special about temperature numbers.
I'd like to be able to monitor the current on a PDU or breaker module to look out for sudden changes.
The situation is this - a cabinet typically operates at a current draw of 6-8 amps per phase... phase 3 has a fairly sudden jump of 3 amps and it stays there for a few days....
even if that isn't causing a problem with my capacity, it is something that would be good to know, if I could get an alert. Right now, I can run a report and look at a trend graph every day, or I can export data and do some manipulation....
But, I don't have any function in DCE that will help me reduce the laborious processes mentioned... I'd like to see a function that allows me to set an alert for sustained load changes that are out of the normal.
(CID:140219797)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:25 PM . Last Modified: β2024-04-03 03:22 AM
Dear Eric Clark,
From your question:
DCE has a function to allow an alarm tied to a rate of change in temperature.
So the function to look at a number and compare it to the number in 5 minutes exists. There is nothing special about temperature numbers.
Do you mean the threshold values Rate of increase and Rate of decrease? If so, then why can't you use the same threshold values for current or power? For example, I have been doing this for a long time.
With respect.
(CID:140707557)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:25 PM . Last Modified: β2024-04-03 03:22 AM
No, you are right, I always get sort of lost in their process of creating alarms - forgot there was an extra layer ... thanks
(CID:140707565)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:25 PM . Last Modified: β2024-04-03 03:22 AM
Dear Stine Hansen,
Tell us please, where did the option for the comment Convert to answer?
Very thanks for the support.
(CID:140707561)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:25 PM . Last Modified: β2024-04-03 03:22 AM
Hi spezialist,
I have changed your comment to an answer.
Thanks,
Stine
(CID:140707567)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:25 PM . Last Modified: β2024-04-03 03:22 AM
Ok, very thanks for the support :-).
(CID:140707717)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:25 PM . Last Modified: β2024-04-03 03:22 AM
Dear Eric Clark,
Tell us, please, did you solve your question or not?
With respect.
(CID:141269255)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 05:25 PM . Last Modified: β2023-10-22 02:21 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.