How can I investigate a failed DCE upgrade? "Unable to upload the server update"

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • How can I investigate a failed DCE upgrade? "Unable to upload the server update"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

0 Likes
12
1636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

How can I investigate a failed DCE upgrade? "Unable to upload the server update"

(CID:89063616)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

0 Likes
2
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi Allan,

 

What version are you on now and what version are you trying to upgrade to? I have seen this happen when the server upgrade package you are using may be corrupt. Did you check the MD5 checksum to see if it is valid? The checksum is on the upgrade link. You can check the file using a program like "Nero MD5 Verifier" . That would be the first step. I have seen the above error happen also when you try and upgrade the server remotely. Are you trying to upgrade the server remotely? Are you using a VPN connection? Have you tried to upgrade the server locally? The logs will tell us more on the issue. If you type in the IP of your DCE server in a web browser followed by /capturelogs (). Delete the old log archive and try to upgrade the server again and then send in the logs after the upgrade. There could potentially be a corruption on the database also. When was the last successful backup carried out? You might also have to import a previous backup and then try an upgrade from the older backup locally. 

Hope this helps. 

 

Regards,

B

(CID:89063618)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

0 Likes
2
1636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi Allan,

 

What version are you on now and what version are you trying to upgrade to? I have seen this happen when the server upgrade package you are using may be corrupt. Did you check the MD5 checksum to see if it is valid? The checksum is on the upgrade link. You can check the file using a program like "Nero MD5 Verifier" . That would be the first step. I have seen the above error happen also when you try and upgrade the server remotely. Are you trying to upgrade the server remotely? Are you using a VPN connection? Have you tried to upgrade the server locally? The logs will tell us more on the issue. If you type in the IP of your DCE server in a web browser followed by /capturelogs (). Delete the old log archive and try to upgrade the server again and then send in the logs after the upgrade. There could potentially be a corruption on the database also. When was the last successful backup carried out? You might also have to import a previous backup and then try an upgrade from the older backup locally. 

Hope this helps. 

 

Regards,

B

(CID:89063618)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

In response to DCIM_Support
0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi Breda, I had a colleague complete this for me. 100% correct advice from you. Thanks. Despite having two upgrades complete remotely, this one didn't like it and only by asking a guy based in the U.S office to run the upgrade id it all run smoothly. thanks again.

(CID:89555053)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

In response to DCIM_Support
0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi Alan, I'm happy this worked for you. Thanks for the update. Regards, B

(CID:89555078)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi Breda,  this is what I've done today.

 

Upgraded from 7.2.0 to 7.2.1. backup taken before and after.

Upgraded from 7.2.1 to 7.2.2 and backup taken.

Attempt to upgrade to 7.2.4 failed.

have downloaded the upgrade zip twice, but haven't checked the md5 checksum.

 

I am doing this over the WAN.

thanks for the quick reply.

regards

Allan

 

(CID:89063620)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:50 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi Breda, I have captured the logs after another failed upgrade attempt.  Please can you advise how I can attach these? 

(CID:89063624)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:39 AM

0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi Allan,

 

I'm unsure of how to attach the logs on this forum. Are you able to send a link to a dropbox account so I can take a look at the logs? 

 

 

Regards,

B

(CID:89063626)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:39 AM

0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi allan.fitzwater and bredaconsidine,

You cannot attach files to the forum, you can however use the "Code Macro"  and paste the contents of your log file. Which will look something like this:

64.242.88.10 - - [07/Mar/2004:16:05:49 -0800] "GET /twiki/bin/edit/Main/Double_bounce_sender?topicparent=Main.ConfigurationVariables HTTP/1.1" 401 12846 64.242.88.10 - - [07/Mar/2004:16:06:51 -0800] "GET /twiki/bin/rdiff/TWiki/NewUserTemplate?rev1=1.3&rev2=1.2 HTTP/1.1" 200 4523 64.242.88.10 - - [07/Mar/2004:16:10:02 -0800] "GET /mailman/listinfo/hsdivision HTTP/1.1" 200 6291 64.242.88.10 - - [07/Mar/2004:16:11:58 -0800] "GET /twiki/bin/view/TWiki/WikiSyntax HTTP/1.1" 200 7352


If the log file is very long i'd suggest that you use a service similar to pastebin and share the link here.

// Viggo

(CID:89063630)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:39 AM

0 Likes
1
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:39 AM

Hi Breda, pls can you try this link.

https://www.dropbox.com/s/0g1msd7abunij91/localhost.grpitsrv.com_2014-07-22_08-38-08.tar.gz

thanks very much.  This isn't urgent so please don't put yourself out!

Lasse - thanks for the info as well.

 

 

(CID:89063635)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:38 AM

In response to DCIM_Support
0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:38 AM

Hi Allan, when answering a question, please comment on "the answer" instead of posting a new answer (that regards a question posted on Jul 22 by Breda), thanks.

(CID:89063769)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:38 AM

0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:38 AM

Hi Allan,

 

Thanks for the logs. There is not much in the info in the logs to go on for the failed upgrade. Did you try and reboot at any stage before trying the upgrade again? Can you try and reboot the server and do the server upgrade again? If this doesn't work I would connect to the server locally rather than trying the upgrade over the network. I have seen problems like this in the past. 

 

Since its an enterprise server. I would connect your laptop to the private side of the server (GB port 2), login to the DCE client on the private side and then try to upgrade the server.  

 

If we are still having problems after this, I would suspect it might be a corruption on the DB.  We might have to do a restore, create a new backup and try to upgrade the server again. 

I hope this helps. 

Regards,

B

(CID:89063642)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:38 AM

0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2024-04-10 01:38 AM

thanks for looking Breda.  I suspect your on to something with my attempt to run it remotely, despite two previous upgrades running smoothly. I tried this AM when our WAN link would be less busy and the progress bar got much much further along.  I'll try rebooting, then running it one more time.  I have also asked a local IT engineer to download and run this for me.  Either way I will update but it may be a couple of weeks due to hols etc.  thanks again.

(CID:89063644)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2023-10-31 11:01 PM

0 Likes
0
1635
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 07:51 AM . Last Modified: ‎2023-10-31 11:01 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore