Hi Allan,
What version are you on now and what version are you trying to upgrade to? I have seen this happen when the server upgrade package you are using may be corrupt. Did you check the MD5 checksum to see if it is valid? The checksum is on the upgrade link. You can check the file using a program like "Nero MD5 Verifier" . That would be the first step. I have seen the above error happen also when you try and upgrade the server remotely. Are you trying to upgrade the server remotely? Are you using a VPN connection? Have you tried to upgrade the server locally? The logs will tell us more on the issue. If you type in the IP of your DCE server in a web browser followed by /capturelogs (
Hope this helps.
Regards,
B
(CID:89063618)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:50 AM . Last Modified: β2024-04-10 01:39 AM
Hi Allan,
What version are you on now and what version are you trying to upgrade to? I have seen this happen when the server upgrade package you are using may be corrupt. Did you check the MD5 checksum to see if it is valid? The checksum is on the upgrade link. You can check the file using a program like "Nero MD5 Verifier" . That would be the first step. I have seen the above error happen also when you try and upgrade the server remotely. Are you trying to upgrade the server remotely? Are you using a VPN connection? Have you tried to upgrade the server locally? The logs will tell us more on the issue. If you type in the IP of your DCE server in a web browser followed by /capturelogs (
Hope this helps.
Regards,
B
(CID:89063618)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:50 AM . Last Modified: β2024-04-10 01:39 AM
(CID:89555053)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:50 AM . Last Modified: β2024-04-10 01:39 AM
(CID:89555078)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:50 AM . Last Modified: β2024-04-10 01:39 AM
Hi Breda, this is what I've done today.
Upgraded from 7.2.0 to 7.2.1. backup taken before and after.
Upgraded from 7.2.1 to 7.2.2 and backup taken.
Attempt to upgrade to 7.2.4 failed.
have downloaded the upgrade zip twice, but haven't checked the md5 checksum.
I am doing this over the WAN.
thanks for the quick reply.
regards
Allan
(CID:89063620)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:50 AM . Last Modified: β2024-04-10 01:39 AM
Hi Breda, I have captured the logs after another failed upgrade attempt. Please can you advise how I can attach these?
(CID:89063624)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:51 AM . Last Modified: β2024-04-10 01:39 AM
Hi Allan,
I'm unsure of how to attach the logs on this forum. Are you able to send a link to a dropbox account so I can take a look at the logs?
Regards,
B
(CID:89063626)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:51 AM . Last Modified: β2024-04-10 01:39 AM
Hi allan.fitzwater and bredaconsidine,
You cannot attach files to the forum, you can however use the "Code Macro" and paste the contents of your log file. Which will look something like this:
If the log file is very long i'd suggest that you use a service similar to pastebin and share the link here.
// Viggo
(CID:89063630)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:51 AM . Last Modified: β2024-04-10 01:39 AM
Hi Breda, pls can you try this link.
https://www.dropbox.com/s/0g1msd7abunij91/localhost.grpitsrv.com_2014-07-22_08-38-08.tar.gz
thanks very much. This isn't urgent so please don't put yourself out!
Lasse - thanks for the info as well.
(CID:89063635)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:51 AM . Last Modified: β2024-04-10 01:38 AM
(CID:89063769)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:51 AM . Last Modified: β2024-04-10 01:38 AM
Hi Allan,
Thanks for the logs. There is not much in the info in the logs to go on for the failed upgrade. Did you try and reboot at any stage before trying the upgrade again? Can you try and reboot the server and do the server upgrade again? If this doesn't work I would connect to the server locally rather than trying the upgrade over the network. I have seen problems like this in the past.
Since its an enterprise server. I would connect your laptop to the private side of the server (GB port 2), login to the DCE client on the private side and then try to upgrade the server.
If we are still having problems after this, I would suspect it might be a corruption on the DB. We might have to do a restore, create a new backup and try to upgrade the server again.
I hope this helps.
Regards,
B
(CID:89063642)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:51 AM . Last Modified: β2024-04-10 01:38 AM
thanks for looking Breda. I suspect your on to something with my attempt to run it remotely, despite two previous upgrades running smoothly. I tried this AM when our WAN link would be less busy and the progress bar got much much further along. I'll try rebooting, then running it one more time. I have also asked a local IT engineer to download and run this for me. Either way I will update but it may be a couple of weeks due to hols etc. thanks again.
(CID:89063644)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 07:51 AM . Last Modified: β2023-10-31 11:01 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.