How can I disable Leak Rope which connected to Netbotz 570 from DCE ?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How can I disable Leak Rope which connected to Netbotz 570 from DCE ?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2024-04-09 04:20 AM

0 Likes
4
550
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2024-04-09 04:20 AM

How can I disable Leak Rope which connected to Netbotz 570 from DCE ?

How can I disable Leak Rope which connected to Netbotz 570 from DCE ? or acknowledge the leak alarm from DCE without log in to Netbotz Advanced View?

Thanks,

Minh 

(CID:99156788)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2024-04-09 04:20 AM

0 Likes
0
551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2024-04-09 04:20 AM

Hi Minh,

 

When you say you want to disable or acknowledge the alarm, are you stating that the alarm condition still exists and you want the alarm to be hidden or are you saying you configured the threshold so that return to normal requires user input?

 

If you configured the threshold to require user input , you can right click the alarm in DCE and choose view alarm details and comments, click details, then click the resolve alarm button. 

 

If you have not used the configuration I noted above and the threshold is still breached (the rope is still wet), you can choose to hide the alarm and the active alarms window will no longer show the alarm. The device in device view however will still show a red X and the NetBotz appliance will still do whatever it's alert profile is configured to do. 

 

If you have the profile set up to send an e-mail until the alarm clears but do not wish to receive repeated e-mails, I suggest using a profile that does not continually alert. The NetBotz appliance will remain in that state until the rope leak dries and that can take some time. There are no set times for the rope to dry as it will depend on temperature, humidity, and how much of the rope was wet.

 

Steve

(CID:99156809)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2024-04-09 04:20 AM

0 Likes
0
551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2024-04-09 04:20 AM

Hi Steve,

Thanks for quick answer.

However, my question is DCE capable of fully control of Netbotz 570  without logging to Advanced View.  

Hopefully, the next version of DCE can.

Thanks,

Minh

(CID:99156820)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2024-04-09 04:20 AM

0 Likes
0
551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2024-04-09 04:20 AM

Hi Minh,

 

Please define the specifics you're looking for. Your initial question only specified information about the leak rope alarm. You did not mention if the alarm was still on, how it was configured, etc. The answer I provided is accurate and if you have the threshold set up on the bot to require user input, clicking resolve on the DCE server clears the alarm in both the DCE server AND the bot.

 

Most other aspects of a Net Botz appliance can be configured through DCE but it's not always as easy as clicking a single button or menu option. There are also certain mass config options on a bot that DCE is either not capable of or, because multiple NetBotz appliances may not all have the same options, you may be able to only configure through DCE a single NetBotz appliance at a time. With this type of config, it may simply be easier to use AV.

 

In any case, you will need to pose a specific question for me to be able to answer it. If you have a specific issue or question, let us know what you're trying to do, what version of DCE and NetBotz including firmware, and we can try to provide an accurate answer. A generalization such as: "is DCE capable of fully control of Netbotz 570 without logging to Advanced View." does not have a simple answer. In most cases the answer is yes. In some minor cases (which may or may not seem minor to you) the answer may be no.

 

Steve

(CID:99156865)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2023-10-31 11:00 PM

0 Likes
0
551
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 02:00 PM . Last Modified: ‎2023-10-31 11:00 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of