How can I Add APC Rack PDU in StruxureWare Data Center 7.2

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How can I Add APC Rack PDU in StruxureWare Data Center 7.2
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
16
3037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

How can I Add APC Rack PDU in StruxureWare Data Center 7.2

I am new to APC StruxureWare Data Center Expert 7.2 which is older version

I want to add devices in it for realtime monitoring. Please guide me how to add following devices?

a. APC Rack PDU Model: A8853

b. PowerLogic PM5560

c. Dell Power Edge 2950 / R620

d. HP Proliant DL G6/G7/G8/G9 Servers

Let me know if additional modules are required for that? Also I want to upgrade the entire StruxureWare Data Center Expert to latest??

 

 

(CID:105457666)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
1
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

Hi Abdullah,

In order to add a device to DCE software, you can follow the instructions provided in the public K-base document ID: FA177081

How to add a device to DCE?

You can add devices by going to “Device-> Add Devices…” in the Data Center Expert client or by right clicking in the monitoring perspective and choosing "Add Devices". 

Add Device–>SNMP v1 or choose the respective protocol type of the device–>Specify the device IP address–>follow the next steps. 

AP8853 uses SNMP v1 or V3. You can choose SNMP v1 by default for AP8853. 

As far as I know, Servers like Dell Power Edge 2950 / R620 and HP Proliant DL G6/G7/G8/G9 Servers are not meant to be monitored in DCE software. 

Reg. DCE software upgrade version, you will need to contact your country technical support for receiving the upgrade version download links. Note: Your DCE software should be under software support contract for receiving the links. 

 

I hope that this helps. 

Regards,

Bala



(CID:105457668)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 16
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
1
3037
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

Hi Abdullah,

In order to add a device to DCE software, you can follow the instructions provided in the public K-base document ID: FA177081

How to add a device to DCE?

You can add devices by going to “Device-> Add Devices…” in the Data Center Expert client or by right clicking in the monitoring perspective and choosing "Add Devices". 

Add Device–>SNMP v1 or choose the respective protocol type of the device–>Specify the device IP address–>follow the next steps. 

AP8853 uses SNMP v1 or V3. You can choose SNMP v1 by default for AP8853. 

As far as I know, Servers like Dell Power Edge 2950 / R620 and HP Proliant DL G6/G7/G8/G9 Servers are not meant to be monitored in DCE software. 

Reg. DCE software upgrade version, you will need to contact your country technical support for receiving the upgrade version download links. Note: Your DCE software should be under software support contract for receiving the links. 

 

I hope that this helps. 

Regards,

Bala



(CID:105457668)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

In response to DCIM_Support
0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

You have provided me enough details. Thank you Balaraman.

(CID:105459525)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

I have added PowerLogic PM5560 power meter, but data is not retrieving from that device to show in DCE. Also please guide me about Email Setting configuration as currently an error appears " Unable to reach SMTP server". How can i verify that the SMTP server ip is pingable from DCE server? Regards, Abdullah Shifa.

(CID:105459528)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

Dear Abdullah, For Power Logic PM5560, I would suggest to verify if the required DDF file is added in DCE in order to view the Device Sensors values in DCE. You can contact Multivendorsupport@apcc.com for the required DDF file depending upon the type of the product(SNMP or Modbus over TCP). Regarding email issue, it could be related to SMTP permission issue. Please check with SMTP server admin to see if the DCE server IP address is white listed. Please also verify if the following details are entered correctly. SMTP Server IP Address SMTP port number Valid Primary DNS and Secondary DNS IP Address Valid Domain Name Does your SMTP require authentication? If so, please enter the authentication details. Also make sure that from email address and DCE IP address are white listed in your exchange server/SMTP server. Secondly, You can refer the below K-base document which can help you to create the email notification policy. FA225766 http://www.apc.com/site/support/us/en/faq/?page=content&country=ITB〈=en&locale=en_US&id=FA225766&red... Regards, Bala

(CID:105459579)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

Thanks for the response. We have now successfully configured SMTP server for email alerts after disabling and changing the Network configuration for Private (LAN2) which conflicts with Public (LAN1).

(CID:105460660)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:33 PM . Last Modified: ‎2024-04-09 01:55 AM

Glad to hear that your issue has been resolved. Have a nice day!

(CID:105460661)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

Dear Bala, "You refer the below K-base document which can help you to create the email notification policy. FA225766" we have read it but we still we are unable to send emails with multiple notification policies to send alerts to different peoples i.e one notification policy has created for Failure and Critical alerts to a group of peoples and second notification policy has created for Warnings, Errors and Critical alerts to another group of people so how can we set multiple notification policies on a same device group?

(CID:105460662)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

Hi Abdullah, I am sorry for the delay in my response. If possible, could you please post your last query as a new query post?

(CID:105461149)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

Hi Bala, We want to create multiple notifications for different threshold to send email on different groups ? How can we do that as we tried but only one notification policy can be assigned on a device group? Example: i.e one notification policy has created for Failure and Critical alerts to a group of peoples and second notification policy has created for Warnings, Errors and Critical alerts to another group of people so how can we set multiple notification policies on a same device group?

(CID:105462472)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

Hi Abdullah, As far as I know in DCE, Custom Thresholds can be associated to multiple Notification Policy. However, Devices can be associated to any one notification policy only.

(CID:105462475)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

This means if we can not apply multiple notification policies to a device group!

(CID:105462476)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

Any other solution for that ???

(CID:105462477)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:55 AM

No, Devices can be associated to a single notification policy. As I mentioned, Custom thresholds which were created for the devices can be associated with multiple notification policy. Therefore, you can create custom thresholds for the devices which can be associated with multiple notification policy.

(CID:105462502)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:54 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:54 AM

so in this regard, we will get emails on different mail groups for multiple threshold!

(CID:105465037)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:54 AM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:34 PM . Last Modified: ‎2024-04-09 01:54 AM

We want to download log files to other system / location on periodic basis for compliance. How can we do that?

(CID:105465038)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:35 PM . Last Modified: ‎2023-10-31 11:00 PM

0 Likes
0
3036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:35 PM . Last Modified: ‎2023-10-31 11:00 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of