I have a HP ProLiant 2500 Gen 8 enclosure with 4 SL210 Gen8 1U Node blades. In the Genome library i find both the SL210 Gen 8 blade and the ProLiant T2500 but the blade wont fit into the chassis. Any suggestions on what might be the reason they don't match?
Regards
André
(CID:93915014)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:30 AM . Last Modified: 2024-04-10 12:52 AM
Hi André,
The reason for the blades not fitting in the enclosure is that the enclosure is a storage enclosure.
The HP ProLiant 2500 Gen 8 enclosure is currently not in the Genome library of DCO.
This means a enclosure must be created manually.
I would recommend creating the enclosure based on the "HP ProLiant BL E-class Server Blade Enclosure"
I added that enclosure to my Genomes and then changed it according to the specs I found giving the following:
Once adding the device to the model it will look something like this where the blades then can be added to the 4 slots/bays by dragging and dropping from the genomes:
(CID:93915081)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:30 AM . Last Modified: 2024-04-10 12:52 AM
Hi André, we will look into it, thanks for sharing.
(CID:93915071)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:30 AM . Last Modified: 2024-04-10 12:52 AM
Hi André,
The reason for the blades not fitting in the enclosure is that the enclosure is a storage enclosure.
The HP ProLiant 2500 Gen 8 enclosure is currently not in the Genome library of DCO.
This means a enclosure must be created manually.
I would recommend creating the enclosure based on the "HP ProLiant BL E-class Server Blade Enclosure"
I added that enclosure to my Genomes and then changed it according to the specs I found giving the following:
Once adding the device to the model it will look something like this where the blades then can be added to the 4 slots/bays by dragging and dropping from the genomes:
(CID:93915081)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:30 AM . Last Modified: 2024-04-10 12:52 AM
Thanx Sören!!
(CID:93915082)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 10:30 AM . Last Modified: 2023-10-31 10:59 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.