Hi Everyone:
By customer requirement we need to deploy GVX, enabled for 18 programmable dry contact. As I understand it is ready for 12 total (6 configurable). I know there is AP9810 for dry contact.
Could you give us a clue to get 18 total configurable, maybe a kind of hub to extend dry contact numbers.
Thank you in advance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-15 08:17 PM
Hi,
Just sharing my thoughts:
1. 2 optional NMC + AP9810 and IO relay from UPS's IO Cabinet (6 programmable).
- Not sure if can support 2 x NMC with 2x AP9810?
2. Get a Modbus controller with programmable output relay. Modbus controller will poll the data from UPS and trigger 18 output relays.
BR,
TJ
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-15 08:17 PM
Hi,
Just sharing my thoughts:
1. 2 optional NMC + AP9810 and IO relay from UPS's IO Cabinet (6 programmable).
- Not sure if can support 2 x NMC with 2x AP9810?
2. Get a Modbus controller with programmable output relay. Modbus controller will poll the data from UPS and trigger 18 output relays.
BR,
TJ