Export all devices configuraiton from DCO or DCE client interface

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Export all devices configuraiton from DCO or DCE client interface
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

0 Likes
6
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

Export all devices configuraiton from DCO or DCE client interface

Asking on behalf of H.B.:

How can I export in a file to be stored for archiving the configuration of each devices referenced into the DCE or into the DCO with only one command / button from the user interface. In case this feature is not currently enable, when it is possible to add it to the DCO / DCE client?

(CID:108828328)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

0 Likes
3
982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

Hi Stine,

 

For DCE, there is a backup option. This option will backup the configuration for use if you need to re-deploy your DCE server. This is not a 1 click option. You must configure a share to store the configuration. The reason for this is that the configuration is on the server and not the client so it's not as easy as a single click export. You must go to system, server administration settings, server backup/restore. You must then add a backup and configure it and a target server appropriately. This backup can then be run on a schedule or on a single click.

 

You can also export saved discoveries. This does not export the list of devices found but you can import this into another DCE server so that you can run the same discoveries from the initial server. Simply right click a discovery and choose export. Select the discoveries to export and click export.

 

Steve

 

(CID:108828339)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

0 Likes
0
982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

Hi H.B. (& Stine)

For DCO, you might want to try the feature "Export Table", that is described here: Exporting Equipment Browser table

 

and for DCE, try the "Export Device List":

(note : only backup files, both for DCO and DCE would contain full configuration of the setup!)
Kind regards

(CID:108828333)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

0 Likes
3
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

Hi Stine,

 

For DCE, there is a backup option. This option will backup the configuration for use if you need to re-deploy your DCE server. This is not a 1 click option. You must configure a share to store the configuration. The reason for this is that the configuration is on the server and not the client so it's not as easy as a single click export. You must go to system, server administration settings, server backup/restore. You must then add a backup and configure it and a target server appropriately. This backup can then be run on a schedule or on a single click.

 

You can also export saved discoveries. This does not export the list of devices found but you can import this into another DCE server so that you can run the same discoveries from the initial server. Simply right click a discovery and choose export. Select the discoveries to export and click export.

 

Steve

 

(CID:108828339)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

In response to DCIM_Support
0 Likes
0
982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:57 AM . Last Modified: ‎2024-04-08 04:20 AM

Thanks for the provided answers. However, it look likes I badly explained my need.

I am not interested with the backup of the DCE / DCO which is already performed through the tools.

However I am considering the discovered devices' individual configuration backup such as the PX, IRC, UPS ...

As I am lazy, I don't want to go through each individual device. Thus, where in DCE / DCO is located such feature?

 

Best regards,

H.B. a.k.a. Hervé Boyer

 

(CID:108828408)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:58 AM . Last Modified: ‎2024-04-08 04:20 AM

In response to DCIM_Support
0 Likes
0
982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:58 AM . Last Modified: ‎2024-04-08 04:20 AM

Hi Herve, 

 

There is currently no option in DCE to export the device's configuration. If you need the files outside of DCE, there is an option on the devices themselves to export the config.ini using ftp.The issue there is that with 6.x firmware, this does not include user info.

 

From within DCE, you can create a template based on the configuration of the device and this basically does the same thing, it saves the configuration of the device on DCE. There is no option however to export it.

 

I can put something like this in as an enhancement request however I do not see something like this getting added to the system any time soon.

 

Steve

(CID:108828663)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:58 AM . Last Modified: ‎2024-04-08 04:20 AM

In response to DCIM_Support
0 Likes
0
982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:58 AM . Last Modified: ‎2024-04-08 04:20 AM

Hello, Thanks for the additional information. Yes please, consider as an enhancement request having an integrated tool into the DCE / DCO allowing to perform the configuration export of all (or partial) the devices configuration. From my point of view, it would also be great having a scheduling option to recurrently export the devices configuration (once a day / week / month). Thanks for the help and support. best regards, Hervé

(CID:108828662)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 06:58 AM . Last Modified: ‎2023-10-22 02:04 AM

0 Likes
0
982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 06:58 AM . Last Modified: ‎2023-10-22 02:04 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore