Emergency help!AP9475 System Restore failed。

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Emergency help!AP9475 System Restore failed。
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:34 PM . Last Modified: ‎2024-04-08 01:54 AM

0 Likes
20
1816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:34 PM . Last Modified: ‎2024-04-08 01:54 AM

Emergency help!AP9475 System Restore failed。

Hi,I met a problem.AP9475 failed to start up and does not work.I made a USB restore mirror, to restore the system through the USB disk.The steps are as follows:

The first step is to turn on the AP9475 server and the screen will look like this:

Select F11 (BIOS Boot Manager)

The system then jumps to the following interface:

chosen UEFI Boot Menu

The system then jumps to the following interface:

chosen Disk connected...

The system then jumps to the following interface:

The final show as shown above, where there is a problem?Looking forward to your reply. Thank you.

Another: System Restore version 7.2.5

(CID:110794857)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 20
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

0 Likes
15
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

Hi Chunyang Niu,

DCE-7.x software and DCE-7.x restore USB-flash aren't able to work with systems in UEFI mode: only the legacy BIOS mode is recognize. Therefore, it is necessary to switch the server to operation in the legacy BIOS mode and only after this to try boot or restore DCE software.

Very thanks for the support.

(CID:110794945)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

In response to DCIM_Support
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

Thanks,then I should choose the"BIOS Boot Menu"?

(CID:110794954)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

In response to DCIM_Support
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

Yes of course.

(CID:110794959)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

In response to DCIM_Support
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

Thank you very much.I'll try.

(CID:110794969)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

In response to DCIM_Support
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

Hi.Thanks for your help.I now have a problem.why the page has been stuck in "anaconda installer init version 13.21.215 using a serial console"

It's been three hours.

(CID:110795310)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

In response to DCIM_Support
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

Whether in that case it is necessary to check in server's BIOS if RS232 serial ports are enabled. Successful installation of DCE-7.x requires availability at least of one RS232 serial port.

(CID:110795330)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

In response to DCIM_Support
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:54 AM

你能告诉我吗 how to do it?I don know  much about the settings of this server.Thanks.

(CID:110795360)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:53 AM

See "Serial Communications" item in BIOS setup.

(CID:110795368)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:35 PM . Last Modified: ‎2024-04-08 01:53 AM

Can you give me a email address?I have a few photos for you to look at.

This affair has trouble me. Hope you can help me.Thanks 

(CID:110795374)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

spezialist@email.ua

(CID:110795386)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

Sorry, do not know what causes the message can not be sent to you. My problem has not been resolved, the following is my shooting BIOS settings picture, please help me look, where there is a problem? Thank you.

(CID:111413508)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

Hi Chunyang Niu,

First report precisely, please, what ISO image or the zip-file you use for creation of the bootable USB stick.

Secondly report precisely their checksums, for example, according to the MD5 protocol.

Only after that it will be possible to continue to understand further.

(CID:111413613)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

Hi all

I am currently having this exact problem on a 20 DCE physical server upgrade project. All the customers existing DCE backups are 7.2.2 and the new AP9475 servers are all 7.2.7. In an effort to minimize data collection loss during the migration process, it would be preferable to flash the new servers to 7.2.2, restore the backup, then upgrade to 7.4.3 straight away or later.

The servers are unable to be flashed via USB to 7.2.2 sticking on the "serial console" message described above. I have ensured that it is set to BIOS boot mode and NOT UEFI and that the serial ports are enabled. 

I have even tried to flash 7.2.1 but the same condition exists. Also tried other AP9475 servers (we have 20) but the same thing.

Is there some incompatibility with these new servers and the Centos OS version that DCE 7.x is built on? 

Regards

Jim Davis - NIE Melbourne/AU

(CID:123343717)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

Hi

As stated above. "I have ensured that it is set to BIOS boot mode and NOT UEFI".

Regards

Jim

(CID:123343722)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

All

Booting from external DVD worked ok and was able to restore 7.2.2 successfully first time. Unsure of the cause for the USB thumb drives not working...

Jim

(CID:123344548)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

Hi Jim Davis,

That's why I wrote, that in some cases it really does require updating the BIOS of the physical server (this is the most correct way).

If for some reason you can not do this and you do not have a DVD drive, in almost such cases I used the Win32 Disk Imager utility. I.e., I just record the iso-image of the DCE-server on the USB stick and that's it. It's very simple, reliable and BIOS independently, especially when you need to update 20 servers and more.

I was glad to help and answer questions.

(CID:123344811)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

0 Likes
1
1813
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:36 PM . Last Modified: ‎2024-04-08 01:53 AM

Dear Chunyang Niu

Could you please confirm the USB restore command prompt status when you created the bootable key? 

Did you see any error similar to the following at the end? If so, then it could be the main cause of the issue for the DCE server not to boot properly to restore. 

Accessing physical drive: Access is denied is related to the USB drive.

There are some google results for the above mentioned error. For example: http://www.howtogeek.com/howto/windows-vista/enable-the-hidden-administrator-account-on-windows-vist...

The clean USB bootable key should not give any error. It should end as shown below. 

With the proper USB restore key, you can just plug it into the DCE server USB port, and then restart the power to the server to restore the DCE image. 

I hope this helps. 

(CID:110795817)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:37 PM . Last Modified: ‎2024-04-08 01:53 AM

In response to DCIM_Support
0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:37 PM . Last Modified: ‎2024-04-08 01:53 AM

Hi,thanks for your help.I have done according to your method, the operation is still shown below:

The problem is where?

In addition, the serial communication settings in the server BIOS are as follows:

How do I set up?

Thanks.

(CID:111413502)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:37 PM . Last Modified: ‎2024-04-08 01:53 AM

0 Likes
0
1814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:37 PM . Last Modified: ‎2024-04-08 01:53 AM

Hi colleagues.

I do not know whether Chunyang Niu found solution this problem, but I already had to update the BIOS and all the built-in hardware components in the appliances AP9465 based on newest DELL servers. 

Jim Davis I do not know which servers are used for you as appliance AP9475, but if there is a above mentioned problem, I would do the following. 

Firstly, you need to try using the USB flash drive to deploy the current version of DCE-7.4.3 (based on CentOS-6.8 x64). In case of failure, try using the DVD drive via USB or via SATA connector (external or internal).

If everything is normal, then, probably, there really is a problem of incompatibility of the newest appliance AP9475 servers with the old version of DCE-7.2.2.

If not, then for verification, you need to try deploying a clean image of CentOS-6.8 x64 or latest CentOS-6.9 x64 in the minimal configuration to your problem server. For deployment at this stage, you must connect a DVD drive via USB or direct via the SATA connector (external or internal).

If everything is fine, then you should try to deploy the OS using USB flesh drive. From my experience I can say that at this stage there can be a failure and then it will really be necessary to update the BIOS of the server to the latest version according to the recommendations of the vendor (DELL, for example).

It is very useful to perform all these preliminary checks to know exactly what the problem is (especially when you have about 20 servers).

Always glad to help and answer questions.

(CID:123344812)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:37 PM . Last Modified: ‎2023-10-22 02:01 AM

0 Likes
0
1812
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:37 PM . Last Modified: ‎2023-10-22 02:01 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of