Ask our Experts
Didn't find what you are looking for? Ask our experts!
Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-10-18 09:40 AM
Hi team,
we have a customer with IT Expert and IT Gateway and it has a lot of alarms of lost network connections with the devices. We would like to increase the timeout in these monitored devices, but we do not see this option in the gateway or in Ecostruxure IT Expert.
Is it possible to increase the timeout in IT Expert? In DCE at least is possible.
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-03 06:40 AM
Hi @jzurera,
Timeouts and retries between the gateway and end devices can be adjusted within the Gateway interface:
Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-03 06:40 AM
Hi @jzurera,
Timeouts and retries between the gateway and end devices can be adjusted within the Gateway interface:
Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.