Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-02-09 11:01 AM
EcoStruxure IT generates an alert when UPS battery power is too low to support the load. However, I would like to receive an alert as soon as a UPS switches to battery power. This will allow us to get ahead of facility power issues. Is there a way to configure EcoStruxure IT for such alerts?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-02-15 01:21 AM
hello,
in DCE, right click on UPs and select create threshold
you can set minimum voltage/range for input,minimum value for battery percent etc
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-02-16 08:46 AM
@Gabi thank you for the reply. The custom threshold is a great idea.
What does DCE stand for?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-02-19 06:33 AM
Hello,
π Data Center Expert initial name of EcoStruxure IT Data Center Expert
so from desktop client software of EcoStruxure IT you can set custom thresholds
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2024-10-22 08:59 AM
Hello @APC_Customer,
It looks like the previous responses to your question may have been around an incorrect product. Your question appears to be based about EcoStruxure IT Expert alerting.
Recently (September 2024) custom thresholding was enabled within ITE and you can use the Duration option for the "Time running on battery" sensor to trigger an email alert.
For details on creating custom thresholds, see https://community.se.com/t5/Alarms/Alarm-threshold-policies-in-IT-Expert/ta-p/485481
Kind Regards,
Cory