Dry contact monitoring

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Dry contact monitoring
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

0 Likes
8
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

Dry contact monitoring

Hi Team,

 

Kindly advice how well I can monitor dry contact devices especially if there are huge number of them in one room mostly UPS, Cooling Units & Automatic Transfer Switches. Should I buy more NetBotz appliances or use the universal sensor ports on the sensor pods which I have read support sensors such as motion detectors, moisture detectors, or glass-break detectors.

 

Regards,

Felix

(CID:93915048)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

Hi Felix!

It's depend of number of dry contacts and Netbotz equipment you already have.

I recommend you to see at NetBotz Rack Monitor 200 (NBRK0200) + Sensor Pod 150 (NBPD0150 ) + Netbotz Dry Contact Cable (NBES0304).

(CID:93915104)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

0 Likes
0
1680
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

I have had four sensors of the same type attached to the same analog sensor pod input. That gave me a generic alert. If you are talking large numbers of sensors then i believe the appropriate route would be to buy APC NetBotz 4-20mA Sensor Pod's which then connect to the rack mount netbotz appliance. That would allow you to customize the alert to match each given sensor.

(CID:93915097)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

0 Likes
0
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

Hi Felix!

It's depend of number of dry contacts and Netbotz equipment you already have.

I recommend you to see at NetBotz Rack Monitor 200 (NBRK0200) + Sensor Pod 150 (NBPD0150 ) + Netbotz Dry Contact Cable (NBES0304).

(CID:93915104)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

0 Likes
2
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

Felix, the two solutions above would definitely work; for high density dry contact monitoring you can also leverage a sealevel device which is supported by Netbotz V2 and V3 devices (400 series and 500 series).  Here is some information on the sealevel device for high density dry contact monitoring.  You can find the company at www.sealevel.com and it would probably be good to call them first if you'd like to utilize this solution:

Hi-Density Dry Contact Monitoring –
NetBotz + SeaI/O-462U

 

The external sensor ports on NetBotz monitoring appliances and Sensor Pods support dry contact sensors.  In applications where customers need to connect a few dry contact sensors, the external sensor ports are a good solution.  However, some applications require connecting large numbers of dry contact sensors to a NetBotz appliance.  In these cases, using the SeaI/O-462U USB to 96 Channel TTL Digital Interface is a more cost-effective solution.

 

The products the customer will need to purchase from SeaLevel Systems (www.sealevel.com) are:

 

SeaI/O-462UUSBto 96 Channel TTL Digital Interface

http://www.sealevel.com/product_detail.asp?product_id=859&USB%5FDigital%5FModbus%5FRTU%5F

 

DB78 to Ribbon Cable (48 connections) – Item# CA237

http://www.sealevel.com/product_detail.asp?product_id=881&%5F

 

Terminal Block Kit (each provides 24 connections) – Item# TB07-KT

http://www.sealevel.com/product_detail.asp?product_id=448&Terminal%5FBlock%5F%2D%5F50%5FPin%2F%5F32%...

 

Power Supply

U.S.:  http://www.sealevel.com/product_detail.asp?product_id=795&%5F

International:  http://www.sealevel.com/product_detail.asp?product_id=792

 

The SeaI/O-462U connects to the NetBotz 500 or 420 via aUSBcable (included with the 462U).  The DB78 to Ribbon Cable connects the SeaI/O-462U to the Terminal Block Kit.

 

Up to 2 SeaI/O-462Us can be connected to a NetBotz 500, and 1 SeaI/O-462U is supported on a NetBotz 420.

 

Note that all ports are configured as inputs when a SeaI/O-462U is connected to a NetBotz appliance (the 462U does have the capability to generate output signals, but this is not supported by the NetBotz appliance).

 

Note that NetBotz also supports the SealevelPIO-48 (Item# 8203) for customers who need high-density dry contact inputs.  

(CID:93915111)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

In response to DCIM_Support
0 Likes
0
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:32 AM . Last Modified: ‎2024-04-10 12:51 AM

Hi Jonathan,

 

I have am using NetBotz 570 & 450, do this support  SeaI/O-462U.

I am very new to this, can you please send me a write up on how you implemented this solution.

 

Regards,

Felix.

 

(CID:94601272)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:33 AM . Last Modified: ‎2024-04-10 12:51 AM

In response to DCIM_Support
0 Likes
0
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:33 AM . Last Modified: ‎2024-04-10 12:51 AM

Hi Felix, the 462U is supported on the 570 and 450. The above text is the best write-up I have but essentially you need on 462U, on DB78 ribbon cable for every 48 dry contacts, and one terminal block for every 24 dry contacts (and a power supply). The 462U plugs directly into the netbotz appliance via USB, the DB78 cable plugs one end into the 462U and has two connections for a terminal block. The terminal blocks offer 24 form C relays (dry contact), I believe you use A, B, and C (8 on each). For support on the Sealevel device, I would recommend an email or call to Sealevel. For help in configuring the Sealevel once connected to Netbotz, I would all into Netbotz support. Sealevel is described in the Netbotz user manual for the two above appliances. Hope this helps

(CID:94601273)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:33 AM . Last Modified: ‎2024-04-10 12:51 AM

0 Likes
0
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:33 AM . Last Modified: ‎2024-04-10 12:51 AM

Hi guys,

 

Thank you all for your generous contributions.

This is very helpful.

 

Regards,

Felix

(CID:93915466)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:33 AM . Last Modified: ‎2024-04-10 12:51 AM

0 Likes
0
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:33 AM . Last Modified: ‎2024-04-10 12:51 AM

Hi Team,

Could you share us all more detail about the installation manual and the instruction (how to connect and configure in netbotz ?)

 

Best regards,

(CID:96044049)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 10:33 AM . Last Modified: ‎2023-10-31 10:56 PM

0 Likes
0
1681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 10:33 AM . Last Modified: ‎2023-10-31 10:56 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of