EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 09:38 AM . Last Modified: β2024-04-10 01:09 AM
I am trying to model a 125kW downflow CRAC but the software seems to limit the cooling to 99.9 kW.
Is there a way around this or a different way to model it?
(CID:93193609)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 09:38 AM . Last Modified: β2024-04-10 01:09 AM
Which version of DCO are you using? On my 7.4 there doesn't seem to be any (practical) limitation.
(CID:93193613)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 09:39 AM . Last Modified: β2024-04-10 01:09 AM
Christian,
I am also on 7.4 and when I try to enter 125kw, it changes the number to 12.5
When I try to increase the number manually by pressing the up arrow, it stops at 100.00
(CID:93193616)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 09:39 AM . Last Modified: β2024-04-10 01:09 AM
(CID:93193630)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 09:39 AM . Last Modified: β2024-04-10 01:09 AM
Hi,
I believe this is limited to 100 kW. There is an enhancement request in the system for this.
Work around: add the device/Downflow CRAC to your room, and then change/set the "Cooling capacity".
Regards,
Breda
(CID:93193620)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 09:39 AM . Last Modified: β2023-10-31 10:55 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.