Detected an unauthorized user attempting to access the SNMP interface

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Detected an unauthorized user attempting to access the SNMP interface
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:00 AM . Last Modified: ‎2024-04-05 03:08 AM

0 Likes
6
3613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:00 AM . Last Modified: ‎2024-04-05 03:08 AM

Detected an unauthorized user attempting to access the SNMP interface

I have a customer that is receiving a cascade of alerts when his monitor servers ping his network management card.

 

I know he can disable this alert but then he won't be able to receive notification in the event of a genuine malicious attack.

 

Is there any way to put is server on a white list to prevent these nuisance e-mails. 

(CID:128065151)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:08 AM

0 Likes
4
3612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:08 AM

Dear Adrian Carroll,

As Steven Marchetti correctly answered, a similar question :

Your first best bet would be to stop the scanning with incorrect credentials...

I.e., in your case, your 3-rd party monitoring server should poll the NMC by the SNMP protocol with the correct community strings (see the settings inside the NMC in the SNMP section).

I hope this is what you need.

With respect.

(CID:128065174)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:08 AM

0 Likes
4
3613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:08 AM

Dear Adrian Carroll,

As Steven Marchetti correctly answered, a similar question :

Your first best bet would be to stop the scanning with incorrect credentials...

I.e., in your case, your 3-rd party monitoring server should poll the NMC by the SNMP protocol with the correct community strings (see the settings inside the NMC in the SNMP section).

I hope this is what you need.

With respect.

(CID:128065174)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:08 AM

In response to DCIM_Support
0 Likes
0
3612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:08 AM

Hi ,

 

The path given by Steven is the path from the DCE. Is there a way to find out the correct community strings from the NMC itself?

(CID:128065951)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:07 AM

In response to DCIM_Support
0 Likes
0
3612
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:07 AM

Dear Adrian Carroll,

...Is there a way to find out the correct community strings from the NMC itself?

Yes, of course.

I explain for SNMPv1: in order for NMC not to flood you with e-mail messages about unauthorized SNMP access attempts, you need to specify the correct Read-only Community Name on your 3-rd party monitoring server for your NMC (please, contact the administrators of this 3-rd party monitoring server).

For example, you need login to the web-GUI of your NMC along the path as in my screenshot (for SNMPv1):

And then we'll see, that for this NMC Read-only Community Name = public (this is the default value, I did not change it, although I could do it). Now, this value, i.e. public must be specified on the 3-rd party monitoring server to poll this your NMC.

If on your 3-rd party monitoring server to poll this NMC is specified the incorrect value of Read-only Community Name, it causes a lot of e-mail messages from the NMC about unauthorized SNMP access attempts.

I hope I understood you correctly and it will help you.

If there are more questions, please ask.

(CID:128065948)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:07 AM

In response to DCIM_Support
0 Likes
0
3613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:07 AM

That's great. Thank you very much for your assistance.

 

(CID:128065943)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:07 AM

In response to DCIM_Support
0 Likes
0
3613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2024-04-05 03:07 AM

Ok, thanks for the feedback 😀.

(CID:128065938)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2023-10-22 01:52 AM

0 Likes
0
3613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:01 AM . Last Modified: ‎2023-10-22 01:52 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore