Hi
is there any way to insert a power limitation to a room?
Example.
i have 4 room and my power is 100kW.
I'd like to set power for
Thanks
(CID:125211127)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-03 11:45 PM . Last Modified: ‎2024-04-05 04:49 AM
Set the input breaker rating at the PDU for the room, with breaker derating.
Set breaker derating at the main PDU output (before racks).
Set design limit on racks within the room
(CID:125211441)