Posted: 2023-01-24 03:40 AM
I running Data Center Expert 7.9.0 and would like to monitor EcoStruxure IT Advisor 9.3.7 via SNMPv3.
I found the following (maybe outdated) guide:
https://helpcenter.ecostruxureit.com/hc/en-us/articles/360038620073-Enabling-IT-Advisor-monitoring-t...
There is a contradiction because in DCE SNMPv3 device add requires two password:
- authentication
- encryption
While ITA webmin requires only one password for SNMPv3 user.
So, how can I add ITA into DCE via SNMPv3?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-24 04:44 AM
Hello Mate
Use the username and password for SNMPv3 as defined in the setup page in webmin. Try authentication type SHA and leave encryption type as none like below.
The above works when I try it with my DCE.
Regards
Greg Sterling
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-24 04:44 AM
Hello Mate
Use the username and password for SNMPv3 as defined in the setup page in webmin. Try authentication type SHA and leave encryption type as none like below.
The above works when I try it with my DCE.
Regards
Greg Sterling