DCO don't display measured temperature values

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO don't display measured temperature values
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:11 AM . Last Modified: ‎2024-04-10 12:38 AM

0 Likes
5
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:11 AM . Last Modified: ‎2024-04-10 12:38 AM

DCO don't display measured temperature values

DCO don't display measured temperature for some racks although there is temperature sensors mapped to the rack. Could anyone advice solution?

(CID:94602765)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:12 AM . Last Modified: ‎2024-04-10 12:38 AM

0 Likes
0
937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:12 AM . Last Modified: ‎2024-04-10 12:38 AM

Hi Valentin,

The measured value is always shown in text below the bar.

The bar is consisting of two elements.

Left side is the calculated temperature which is based on

  • Max target inlet temperature (can be set in Room properties under Cooling)
  • Cooler supply temperature (can be set in Room properties under Cooling)
  • Measured inlet temperature for the rack (can be set in Rack properties under Cooling)

The right side of the bar is measured temperature of the rack

  • The highest associated sensor temperature in the rack

What is experienced and the reason why sometimes the measured bars are not shown is the fact that the calculated values are setting the boundaries for what is shown.

This means that you might experience that having a measured value that is not within the same range as the numbers used for the calculated values will result in the measured bar not be drawn but only the value to be shown as a number.

I will continue to investigate a bit further and update the thread once more information is found.

(CID:94602981)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:11 AM . Last Modified: ‎2024-04-10 12:38 AM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:11 AM . Last Modified: ‎2024-04-10 12:38 AM

Hi Valentin, If you want to see the temperature sensors you will need to select the rack as you did the in picture number 2. To me it looks like you have the measured inlet temperature on both pictures. In picture number 1: what happens if you select the rack? (rack will be seen in the right side of the screen.). Do you see the attached sensors ? Are the sensors placed in the front of the rack? In case they are not reading data but still attached would the sensors show a "?". Please elaborate on the error you are experiencing. Thanks Jesper

(CID:94602781)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:11 AM . Last Modified: ‎2024-04-10 12:38 AM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:11 AM . Last Modified: ‎2024-04-10 12:38 AM

Hi Jesper! Thanks for your answer! I asked the question wrong, sorry... It might be like "DCO dont display measured temperature diagram" Yes, we have measured values from sensors, but in one rack it shows as green bar near calculated temperature, and in other - not. May be it is an improperly scaling or something like this?

(CID:94602806)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:12 AM . Last Modified: ‎2024-04-10 12:38 AM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:12 AM . Last Modified: ‎2024-04-10 12:38 AM

Hi Valentin,

The measured value is always shown in text below the bar.

The bar is consisting of two elements.

Left side is the calculated temperature which is based on

  • Max target inlet temperature (can be set in Room properties under Cooling)
  • Cooler supply temperature (can be set in Room properties under Cooling)
  • Measured inlet temperature for the rack (can be set in Rack properties under Cooling)

The right side of the bar is measured temperature of the rack

  • The highest associated sensor temperature in the rack

What is experienced and the reason why sometimes the measured bars are not shown is the fact that the calculated values are setting the boundaries for what is shown.

This means that you might experience that having a measured value that is not within the same range as the numbers used for the calculated values will result in the measured bar not be drawn but only the value to be shown as a number.

I will continue to investigate a bit further and update the thread once more information is found.

(CID:94602981)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:12 AM . Last Modified: ‎2024-04-10 12:38 AM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:12 AM . Last Modified: ‎2024-04-10 12:38 AM

Thank you, Soren!

Your answers always very helpful!

(CID:94603068)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:12 AM . Last Modified: ‎2023-10-31 10:49 PM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:12 AM . Last Modified: ‎2023-10-31 10:49 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of