DCO desktop client - How to open all server/storage room

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • DCO desktop client - How to open all server/storage room
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:19 PM . Last Modified: ‎2024-04-03 12:30 AM

0 Likes
4
1026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:19 PM . Last Modified: ‎2024-04-03 12:30 AM

DCO desktop client - How to open all server/storage room

Hi,

In DCO desktop client how can I open all server/storage room?

Background info: I have 100+ server/storage and I have to search by serial numbers in the entire DCO database. The result devices will be update with a "Edit mutiple item" feature.

Is there any other way to achieve this goal?

Thanks.

(CID:149291040)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:19 PM . Last Modified: ‎2024-04-03 12:30 AM

0 Likes
2
1026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:19 PM . Last Modified: ‎2024-04-03 12:30 AM

Hi Mate,

I would use the Inventory search feature in the Web-client:

I understand that suing the web-client while working on the desktop client might be an extra work, but opening 100+ rooms (not recommended) might affect the server/client performance.

Furthermore, REST api "GET /assets/search" can also be used to search for assets containing the words in the string (such as serial number).

Kind regards 

(CID:149291081)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:19 PM . Last Modified: ‎2024-04-03 12:30 AM

In response to DCIM_Support
0 Likes
0
1026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:19 PM . Last Modified: ‎2024-04-03 12:30 AM

Hi Jef,

See my last sentence: (and sorry for the typo) The result devices will be updated with "Edit mutiple item" feature.

More details: I have to use a long key string for search like: "serial1 OR serial2 OR serial3....."

Web interface doesn't allow to use boolen strings in search. Furthermore let's say I have 98 results of the search. I want to update each of 98 items with the same property value, using the "Edit multiple item" feature which is available in the desktop version.

Do you think it is feasible with REST API?

(CID:149291143)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:19 PM . Last Modified: ‎2024-04-03 12:30 AM

In response to DCIM_Support
0 Likes
0
1026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:19 PM . Last Modified: ‎2024-04-03 12:30 AM

Hi Mate,

Sorry, currently that's not possible - searching and/or editing multiple items in web-client/rest api is currently unsupported. As a part of near future road map it is expected to move most (or all) of desk-top client functionality gradually to web-client. This multi edit feature most likely could/would be part of the re-thinking and further development for the web-client.

Kind regards

(CID:149291169)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-05 10:20 PM . Last Modified: ‎2023-10-22 01:44 AM

0 Likes
0
1026
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-05 10:20 PM . Last Modified: ‎2023-10-22 01:44 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore