The simple PUE configuration has a place for sensor measurements for total facility load (Power in) and IT load. How is this accomplished when configuring energy systems within the energy efficiency configuration. In the configuration tips it states "
4. SwitchgearOnly one switchgear should be used in a energy system in Energy Efficiency, even if several switchgears exits in the data center configuration.
Switchgears can only be estimated. It is possible to add a script to a switchgear, but it will not be taken into account in the PUE calculation. "
Thanks
(CID:106891115)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:35 AM . Last Modified: β2024-04-08 11:37 PM
Dear Tony,
Please refer the below post which describes the tips for configuring Energy Efficiency.
Tips for configuring Energy Efficiency
Total Facility Load = IT Load + sum of losses of all subsystems
-> For a switchgear, PDU, UPS : loss = difference in KW between the input and the output of the subsystem. Subsystem losses are calculated either from real measurement (scripts) or from an estimation from a model of the subsystem (Energy Efficiency properties of the subsystem). Note that a script returns the INPUT value of the subsystem.
-> Cooling units, lighting, ventilation and infiltration are considered as 100% losses.
This means that energy efficiency module does not actually calculate the PUE as a ratio of input power and IT Load.
I hope this helps.
regards,
Bala
(CID:106891118)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:35 AM . Last Modified: β2024-04-08 11:37 PM
Dear Tony,
Please refer the below post which describes the tips for configuring Energy Efficiency.
Tips for configuring Energy Efficiency
Total Facility Load = IT Load + sum of losses of all subsystems
-> For a switchgear, PDU, UPS : loss = difference in KW between the input and the output of the subsystem. Subsystem losses are calculated either from real measurement (scripts) or from an estimation from a model of the subsystem (Energy Efficiency properties of the subsystem). Note that a script returns the INPUT value of the subsystem.
-> Cooling units, lighting, ventilation and infiltration are considered as 100% losses.
This means that energy efficiency module does not actually calculate the PUE as a ratio of input power and IT Load.
I hope this helps.
regards,
Bala
(CID:106891118)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:35 AM . Last Modified: β2023-10-31 10:49 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.