Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84244members
353342posts

DCO Power Capacity and Portlets

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
3
365

DCO Power Capacity and Portlets

This question was originally posted on DCIM Support by Brian Meade on 2018-03-23


Hello,

I have a question concerning DCO 8.2.2 and StruxureWare Portal 1.3.7. I have configured several portlets concerning power capacity and due to estimated load and the lack of measured data the power consumption is listed at 100%. However, I have measured PDU(s) and UPS systems.

  1.  If a measured UPS is associated with the UPS(s) of a location within DCO will the portal display the measured value if or is the portlet only using the estimated load values? 
  2. If not is there an alternative portlet that can give a percentage of total power consumption? If not my only option is to use DCE sensor values which are ok, but only show the measured value and not total available capacity in comparison to consumption.

 

(CID:129411258)

3 Replies 3
DCIM_Support
Picard
Picard
0 Likes
1
365

Re: DCO Power Capacity and Portlets

This answer was originally posted on DCIM Support by Christopherus Laurentius on 2018-03-24


Hi Brian,

You may want to use 'Predicted Power' to get DCO Power capacity to use measured power whenever available, instead of estimated load.

To achieve predicted power to be as close as measured power, set the lower & upper threshold as 1.

See here to read more on Predicted Power

About predicted power

(CID:129411274)

DCIM_Support
Picard
Picard
0 Likes
0
365

Re: DCO Power Capacity and Portlets

This comment was originally posted on DCIM Support by Waseem Khan on 2018-03-25


Jef Faridi I have somewhat same concern the power capacity is calculated based on the nameplate of the equipment's

Mobily has more than 10,000 equipment's in one data center, it is impossible to get the accurate values of each equipment and that is why the power capacity gets wrong

Please i need your support in this matter that how can we get the accurate power capacity as well as cooling capacity

PS: we have sensors on ups,pdu,rectifiers and on power panels but when we connected the power path and because of the wrong nameplate KW value on equipment's the power is exceeding on ups,pdu and power panel.

There is a huge difference between the sensor value and the actual value from nameplate

Pls suggest

Thanks