DCO LAB
Hi,
How do I give users permissions to use DCO lab to run simulations without giving them Permissions to amended the Live environment?
Martin
(CID:121210812)
- Labels:
-
Data Center Operation
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:18 PM . Last Modified: 2024-04-08 12:15 AM
Browse to DCO web page (not webmin)
login as an administrator
find the user
Select
Set to View
Then allow "Data Center Lab" under Global Permissions - Access To:
You of course need a SXW DCO:Capacity License
Cheers
(CID:121211079)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:18 PM . Last Modified: 2024-04-08 12:15 AM
Browse to DCO web page (not webmin)
login as an administrator
find the user
Select
Set to View
Then allow "Data Center Lab" under Global Permissions - Access To:
You of course need a SXW DCO:Capacity License
Cheers
(CID:121211079)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:18 PM . Last Modified: 2024-04-08 12:15 AM
Thank you for your response, thats working perfectly 😀
(CID:121211342)
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:18 PM . Last Modified: 2023-10-22 01:38 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.