After I identify higher than expected peak power display in the branch circuit in PDU, I have changed the trending setting to its lowest value which is 2 days. However, after 2 days or even 1 week, the same expected peak is still displayed even though the DCE history the peak is much less than what is displayed.
Is there a way to flush the history and start again ? or there is another setting controlling this peak value displayed?
(CID:147195408)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:41 PM . Last Modified: 2024-04-03 01:07 AM
Hi Jimmy,
Power info (peak and avg.) displayed in DCO are the result of power data calculations over the user defined period (default 30 days). This time period (7 days is the minimum) can be modified in DCO desktop client by editing the integrated DCE in System Setup > External Systems Configuration (https://sxwhelpcenter.ecostruxureit.com/display/UADCO8x/Configuring+StruxureWare+Data+Center+Expert+...).
Kind regards
(CID:147195612)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 08:41 PM . Last Modified: 2023-10-22 01:37 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.