DCO-DCE external system data prerequisites?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO-DCE external system data prerequisites?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:16 PM . Last Modified: ‎2024-04-08 12:16 AM

0 Likes
6
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:16 PM . Last Modified: ‎2024-04-08 12:16 AM

DCO-DCE external system data prerequisites?

DCE is configured in DCO as an external devices to get all our PDU and ATS sensor data

But after device assocations only a few PDU display mesured data. What are the prerequisites in DCE to display power data in DCO? Do the related ddf file of the PDU need to be reviewed?

(CID:120817322)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2024-04-08 12:15 AM

0 Likes
1
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2024-04-08 12:15 AM

Hi Yannick

See https://hlep.se-dmaas.com/display/DCIMDEVELOPER/DCE+Sensor+Mapping+to+DCO

From the ISXCSensorType, a subset of the sensors are mapped in DCO for temperature and power.

Power Sensors:

OUTPUT_POWER_WATTS

OUTPUT_POWER_TOTAL_WATTS

MODULE_OUTPUT_POWER or MODULE_BREAKER_POWER

The only way IO know to absolutely prove that DCE is or is not exposing the exact sensors via teh web service API is to query it.  You can do this by downloading free SoapUI (soapui.org) and then installing the relevant WSDLs form

http://sxwhelpcenter.ecostruxureit.com/display/public/UADCE725/StruxureWare+Data+Center+Expert+Web+S...

ISXCentralDeviceGroupService_v2_0

ISXCentralDeviceService_v2_0
ISXCentralSensorService_v2_0

If you find an issue, you can then go back to multivendorsupport@apc.com and describe exactly what you need.  I know that may be a lot but it's the only way for you to be sure.  

Otherwise, you can go back to multivendorsupport@apc.com and ask for the DDFs that will properly expose the data to DCO

Cheers 

(CID:121211073)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:16 PM . Last Modified: ‎2024-04-08 12:16 AM

0 Likes
1
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:16 PM . Last Modified: ‎2024-04-08 12:16 AM

Hi Yannick

The presence of the device in DCE does not guarantee it will be properly shown in DCO.  This is dependant on the DDF which must be code to present data to DCO in the correct format.  I recall a EcoStruxure IT Help Center post about DDF and DCO but in any event, you should make sure time sync is OK

http://sxwhelpcenter.ecostruxureit.com/display/public/UADCO8x/The+Importance+of+System+Time+Synchron...

and give DCO 24 hours.

You did not mention make and model of rPDU.  IF they are late model APC with latest firmware and DDF it often works OOB (but sometimes needs a little DDF caress)

Cheers

Ed

(CID:120817331)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:16 PM . Last Modified: ‎2024-04-08 12:15 AM

In response to DCIM_Support
0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:16 PM . Last Modified: ‎2024-04-08 12:15 AM

Hi Ed,

Thanks. I already know this post.

We are using different models of rPDU: IBM, Liebert Emerson

The sensors are displayed in DCO only for IBM DPI C13 pdu.

In DCO which data is got from DCE? Is it based on a specific sensor name?

I have noticed the IBM PDU have a sensor, named "PDU Output Total Power" that is diplayed in DCO as "Peak Power". With the current ddf file, the Emerson PDU do not have this kind of sensor, or less explicit "MPH2 1 - Power Source 1 - Power Total"...

Regards,

Yannick

(CID:121210959)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2024-04-08 12:15 AM

0 Likes
1
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2024-04-08 12:15 AM

Hi Yannick

See https://hlep.se-dmaas.com/display/DCIMDEVELOPER/DCE+Sensor+Mapping+to+DCO

From the ISXCSensorType, a subset of the sensors are mapped in DCO for temperature and power.

Power Sensors:

OUTPUT_POWER_WATTS

OUTPUT_POWER_TOTAL_WATTS

MODULE_OUTPUT_POWER or MODULE_BREAKER_POWER

The only way IO know to absolutely prove that DCE is or is not exposing the exact sensors via teh web service API is to query it.  You can do this by downloading free SoapUI (soapui.org) and then installing the relevant WSDLs form

http://sxwhelpcenter.ecostruxureit.com/display/public/UADCE725/StruxureWare+Data+Center+Expert+Web+S...

ISXCentralDeviceGroupService_v2_0

ISXCentralDeviceService_v2_0
ISXCentralSensorService_v2_0

If you find an issue, you can then go back to multivendorsupport@apc.com and describe exactly what you need.  I know that may be a lot but it's the only way for you to be sure.  

Otherwise, you can go back to multivendorsupport@apc.com and ask for the DDFs that will properly expose the data to DCO

Cheers 

(CID:121211073)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2024-04-08 12:15 AM

In response to DCIM_Support
0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2024-04-08 12:15 AM

Hi Ed,

Thanks a lot. I investigated and in fact the ISXCSensorType of the Total Power sensor on the Liebert Emerson rPDU is UNKNOWN unlike the IBM rPDU where it is correctly OUTPUT_POWER_TOTAL_WATTS

I will then contact the support

Cheers

Yannick

(CID:121211206)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2024-04-08 12:15 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2024-04-08 12:15 AM

FYI to colleagues Daniel Kwong Eddie Mou Fergus Wong Edward Chan

This is the DCE=> DCO data linkage technical discussion. If we are interfacing with external BMS system via DCE first then to DCO, in-depth understanding and insight into items in this discussion are needed.

This DCE=>DCO data linkage is just 1 part of the full story-chain. We still have

  • BMS=>DCE - for Bacnet, we may need Automation Server (AS-P) help. For dry contact, we may need Netbotz etc.
  • Modbus Slave device requirement of DCO for proper modeling - We may need 3rd party connector to help convert Modbus TCP Client into multiple Modbus TCP Slave

 

(CID:132669191)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2023-10-22 01:36 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:17 PM . Last Modified: ‎2023-10-22 01:36 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of