DCE is configured in DCO as an external devices to get all our PDU and ATS sensor data
But after device assocations only a few PDU display mesured data. What are the prerequisites in DCE to display power data in DCO? Do the related ddf file of the PDU need to be reviewed?
(CID:120817322)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:17 PM . Last Modified: β2024-04-08 12:15 AM
Hi Yannick
See https://hlep.se-dmaas.com/display/DCIMDEVELOPER/DCE+Sensor+Mapping+to+DCO
From the ISXCSensorType, a subset of the sensors are mapped in DCO for temperature and power.
Power Sensors:
OUTPUT_POWER_WATTS
OUTPUT_POWER_TOTAL_WATTS
MODULE_OUTPUT_POWER or MODULE_BREAKER_POWER
The only way IO know to absolutely prove that DCE is or is not exposing the exact sensors via teh web service API is to query it. You can do this by downloading free SoapUI (soapui.org) and then installing the relevant WSDLs form
ISXCentralDeviceGroupService_v2_0
ISXCentralDeviceService_v2_0
ISXCentralSensorService_v2_0
If you find an issue, you can then go back to multivendorsupport@apc.com and describe exactly what you need. I know that may be a lot but it's the only way for you to be sure.
Otherwise, you can go back to multivendorsupport@apc.com and ask for the DDFs that will properly expose the data to DCO
Cheers
(CID:121211073)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:16 PM . Last Modified: β2024-04-08 12:16 AM
Hi Yannick
The presence of the device in DCE does not guarantee it will be properly shown in DCO. This is dependant on the DDF which must be code to present data to DCO in the correct format. I recall a EcoStruxure IT Help Center post about DDF and DCO but in any event, you should make sure time sync is OK
and give DCO 24 hours.
You did not mention make and model of rPDU. IF they are late model APC with latest firmware and DDF it often works OOB (but sometimes needs a little DDF caress)
Cheers
Ed
(CID:120817331)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:16 PM . Last Modified: β2024-04-08 12:15 AM
Hi Ed,
Thanks. I already know this post.
We are using different models of rPDU: IBM, Liebert Emerson
The sensors are displayed in DCO only for IBM DPI C13 pdu.
In DCO which data is got from DCE? Is it based on a specific sensor name?
I have noticed the IBM PDU have a sensor, named "PDU Output Total Power" that is diplayed in DCO as "Peak Power". With the current ddf file, the Emerson PDU do not have this kind of sensor, or less explicit "MPH2 1 - Power Source 1 - Power Total"...
Regards,
Yannick
(CID:121210959)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:17 PM . Last Modified: β2024-04-08 12:15 AM
Hi Yannick
See https://hlep.se-dmaas.com/display/DCIMDEVELOPER/DCE+Sensor+Mapping+to+DCO
From the ISXCSensorType, a subset of the sensors are mapped in DCO for temperature and power.
Power Sensors:
OUTPUT_POWER_WATTS
OUTPUT_POWER_TOTAL_WATTS
MODULE_OUTPUT_POWER or MODULE_BREAKER_POWER
The only way IO know to absolutely prove that DCE is or is not exposing the exact sensors via teh web service API is to query it. You can do this by downloading free SoapUI (soapui.org) and then installing the relevant WSDLs form
ISXCentralDeviceGroupService_v2_0
ISXCentralDeviceService_v2_0
ISXCentralSensorService_v2_0
If you find an issue, you can then go back to multivendorsupport@apc.com and describe exactly what you need. I know that may be a lot but it's the only way for you to be sure.
Otherwise, you can go back to multivendorsupport@apc.com and ask for the DDFs that will properly expose the data to DCO
Cheers
(CID:121211073)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:17 PM . Last Modified: β2024-04-08 12:15 AM
Hi Ed,
Thanks a lot. I investigated and in fact the ISXCSensorType of the Total Power sensor on the Liebert Emerson rPDU is UNKNOWN unlike the IBM rPDU where it is correctly OUTPUT_POWER_TOTAL_WATTS
I will then contact the support
Cheers
Yannick
(CID:121211206)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:17 PM . Last Modified: β2024-04-08 12:15 AM
FYI to colleagues Daniel Kwong Eddie Mou Fergus Wong Edward Chan
This is the DCE=> DCO data linkage technical discussion. If we are interfacing with external BMS system via DCE first then to DCO, in-depth understanding and insight into items in this discussion are needed.
This DCE=>DCO data linkage is just 1 part of the full story-chain. We still have
(CID:132669191)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 05:17 PM . Last Modified: β2023-10-22 01:36 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.