DCO Connection Error

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO Connection Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:48 AM . Last Modified: ‎2024-04-08 11:13 PM

0 Likes
8
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:48 AM . Last Modified: ‎2024-04-08 11:13 PM

DCO Connection Error

Dear Team, 

I am having a connection error from one of my customer. I am able to ping the server but having the attached error's.  Also I am not able to reach webmin to collect the log files. Looking for advises. 

Thanks in advance. 

 

Best regards. 

(CID:108824640)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

0 Likes
6
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

Hi Behram, If you are not able to reach the server via webmin, then it might be network related or perhaps 'DCO server' is not running (ping will only confirm that the host/server is alive/online, but it cannot say anything about its functionality/operation) ... Perhaps the server have been disconnected and reconnected, if so rebooting might be needed. Can you try from another workstation and see if you can reach the server both via webmin and ssh access (via Putty or similar tool). Is this a physical server or running on VM? (verify if the server is okay, you might see warnings on its console). Kind regards

(CID:108827834)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

Hi Jef, Thanks a lot for your quick response. The setup is on VM and I just checked the SSH access and it is working fine. How can we test that server is working properly ? What kind of comment do we need? Server seems ok but still have the same error. Best regards

(CID:108827836)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

Hi Behram, I would at least try "sudo service operations status", that would inform if the Operations is running. Did you try to test the connection (Webmin and/or dco client) from another workstation? Basically you would need to access the Webmin (try from different workstations "close" to server - excluding the network/routing issues), if not accessible, then ssh login, and "reboot". Please let me know how it goes, thanks Kind regards

(CID:108827838)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

Hi Behram, I was wondering how it goes and if the issue is resolved? Kind regards

(CID:108827840)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

Dear Jef, Sorry for my late response, but the customer is not reachable for last 2-3 weeks. The issue is still on going and even we do the reboot from vm consoles and etc. Having the same. By the we are not able to reach from putty from the client pc this an another interesting point. We are able to open the https://#dcoip/ but not able to go further. I am connected to customer via webex. Do you have time to take a look ? Best regards

(CID:108828407)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

Hi Behram, No problem. I can take a look, please email me the webex link and phone no, thanks. Kind regards

(CID:108828412)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

In response to DCIM_Support
0 Likes
0
1188
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2024-04-08 11:13 PM

Hi Behram, Many thanks for the meting this morning - just a short note to share with you/community that basically the issue was/is disk space related (the current setup has too little disc capacity and is full). Customer will 'upgrade' the setup based on system recommendations (using at least 100 GB storage). It was suggested that they will go for the latest version (currently DCO 8.0.1). Kind regards

(CID:108828491)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2023-10-31 10:48 PM

0 Likes
0
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 05:49 AM . Last Modified: ‎2023-10-31 10:48 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of