EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:50 PM . Last Modified: 2024-04-03 11:45 PM
I did a clean install from DCO 8.2.12 ISO.
I use NFS share for backups but I was not able to mount from webadmin.
The problem is the same like I reported 2 years ago:
DCO 8.0.1 unable to mount NFS share
It means "nfs_utils" is still missing from CentOS image.
(CID:137106421)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:51 PM . Last Modified: 2024-04-03 11:45 PM
Hi Mate,
To install the nfs-utils, ssh log in to server, and then run the following command:
sudo yum -y install nfs-utils
Kind regards
(CID:137106766)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:51 PM . Last Modified: 2024-04-03 11:45 PM
Hi Jef,
I know, just wondering why this basic package is not part of DCO installation media which based on CentOS 7.
Thank you.
(CID:137108838)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 02:51 PM . Last Modified: 2023-10-22 01:32 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.