DCO 8.1, Placement Advisor - Watts per U Height?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCO 8.1, Placement Advisor - Watts per U Height?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

0 Likes
4
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

DCO 8.1, Placement Advisor - Watts per U Height?

I'm trying to use the asset provisioning tool in DCO 8.1 and for some reason almost every rack always has "Watts Per U Height" as yellow or red, never green, even in a completely empty rack, regardless of what equipment I choose.

 

 

can anyone explain this recommendation better and what it would it requires for it show green instead of yellow?  In my example above, I was using a 300 W server and 8.6 kw rack pdus

(CID:119050632)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

0 Likes
1
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

My best guess is that Operations is warning you that if you continue to add 185W servers (as is the load shown in the screenshot) you will run out U-space before using all the capacity in the rack.

44 servers of 185W: 8.14 kW

Capacity of each rack PDU: 8.6 kW

Hope this helps.

Best,

Niels

(CID:119050828)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

0 Likes
1
897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

My best guess is that Operations is warning you that if you continue to add 185W servers (as is the load shown in the screenshot) you will run out U-space before using all the capacity in the rack.

44 servers of 185W: 8.14 kW

Capacity of each rack PDU: 8.6 kW

Hope this helps.

Best,

Niels

(CID:119050828)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

In response to DCIM_Support
0 Likes
0
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

Thank you both, Niels was right, changing it to a 500w 1U server made some green racks.  I assume there isn't way to disable/ignore specific placement advisor suggestions is there?

(CID:120129569)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

0 Likes
0
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2024-04-08 12:38 AM

As Niels pointed out, "Watts Per U Height" is there to avoid stranded power capacity, if you try with a 1U server of 500W the "Watts Per U Height" should go green.

Or if you do not intend to use the full rack PDU capacity in a rack, you could set a design limit on the rack, which more matches the "power use" of servers you want to use.

BTW: "Watts Per U Height" never goes red, so the red racks are caused by something else.

 

Best,

Gert

 

(CID:119050977)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2023-10-22 01:31 AM

0 Likes
0
896
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 PM . Last Modified: ‎2023-10-22 01:31 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of