Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84766members
354198posts

DCO 3D temp. issue

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
DCIM_Support
Picard
Picard
0 Likes
4
293

DCO 3D temp. issue

This question was originally posted on DCIM Support by Chu Li Wei on 2018-04-23


Hi Team ,

We config DCO and showed 2D was very well . When turn to 3D mode , it's showed cooling is not

enough ,the temp. may incorrect . I'm tring to add more cooling but the result was the same ,

can someone advice what's the problem'on it ? Many thanks.

Best Regards

 

(CID:130098033)


Accepted Solutions
DCIM_Support
Picard
Picard
0 Likes
2
293

Re: DCO 3D temp. issue

This answer was originally posted on DCIM Support by Christopherus Laurentius on 2018-04-23


Billy,

Your cold aisle containment need to cover the rack, not only till the front door of the rack

Look at the video example around 6 minute on how to model the containtment.

The video showed hot aisle containment, but the method is the same.

http://sxwhelpcenter.ecostruxureit.com/display/VIDEO/How+to+model+different+types+of+cooling

 

(CID:130098046)

See Answer In Context

4 Replies 4
DCIM_Support
Picard
Picard
0 Likes
2
294

Re: DCO 3D temp. issue

This answer was originally posted on DCIM Support by Christopherus Laurentius on 2018-04-23


Billy,

Your cold aisle containment need to cover the rack, not only till the front door of the rack

Look at the video example around 6 minute on how to model the containtment.

The video showed hot aisle containment, but the method is the same.

http://sxwhelpcenter.ecostruxureit.com/display/VIDEO/How+to+model+different+types+of+cooling

 

(CID:130098046)

DCIM_Support
Picard
Picard
0 Likes
0
293

Re: DCO 3D temp. issue

This comment was originally posted on DCIM Support by Chu Li Wei on 2018-04-24


Hi Chris ,

Thank you ,I will check it later .

Best Regards

(CID:130098674)

DCIM_Support
Picard
Picard
0 Likes
0
293

Re: DCO 3D temp. issue

This comment was originally posted on DCIM Support by Chu Li Wei on 2018-04-24


Hi Chris ,

Thank you ,I will check it later .

Best Regards

(CID:130098675)

DCIM_Support
Picard
Picard
0 Likes
0
293

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.