I have a client with 9 x Netbotz 250's, all with rack access equipment installed.
He would like to know if the card ID's can be set up with Active Directory, or if they all need to be configured manually.
(CID:130097946)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:45 PM . Last Modified: 2024-04-05 12:08 AM
HI Paul!
Netbotz 250 can not be directly intgrated with AD.
Using RADIUS server authentification can be an option in your case.
You need to switch on RADIUS autentification in Rack Access settings and configure dictionary and user files.
(CID:130097958)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:45 PM . Last Modified: 2024-04-05 12:08 AM
HI Paul!
Netbotz 250 can not be directly intgrated with AD.
Using RADIUS server authentification can be an option in your case.
You need to switch on RADIUS autentification in Rack Access settings and configure dictionary and user files.
(CID:130097958)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:45 PM . Last Modified: 2024-04-05 12:08 AM
Cool, thanks for the answer Valentin
(CID:130682401)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:45 PM . Last Modified: 2023-10-22 03:16 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.