So according to my DCE Modbus TCP device list, DCE only scans the Modbus devices once a day.
Any thoughts on this? How to troubleshoot?
Regards,
J
(CID:130097691)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:08 AM
Dear John Smith,
An interesting problem... What is your version of DCE software?
Have you tried restarting the DCE server?
Can you do DCE capture logs according to topic ?
Can you then analyze the text file /var/log/messages and identify any errors or problems with your TCP/IP Modbus device (by its IP address and Slave ID)?
With respect and wait for your answer.
(CID:130681868)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:09 AM
Hi John Smith, thanks for posting. Let's hope you find your answer here.
Kind regards Ditte
(CID:130099183)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:08 AM
Dear John Smith,
Please describe in detail your question: do you want to poll the TCP/IP Modbus devices only once a day, or does your DCE-server have problems with the polling interval of the TCP/IP Modbus devices?
With respect.
(CID:130680473)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:08 AM
My DCE only scans the devices once a day and I would like them to scan on the interval chosen (every 5 minutes).
When I look at the "Last Scan Time" it usually only shows once in the morning and that is it. Looking at the trend graphs, it shows the data point only once a day...
DCE is NOT scanning the device every 5 minutes as it should.
(CID:130680960)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:08 AM
Dear John Smith,
An interesting problem... What is your version of DCE software?
Have you tried restarting the DCE server?
Can you do DCE capture logs according to topic ?
Can you then analyze the text file /var/log/messages and identify any errors or problems with your TCP/IP Modbus device (by its IP address and Slave ID)?
With respect and wait for your answer.
(CID:130681868)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:08 AM
Apparently there is a Known Modbus Scanner issue which was fixed in DCE 7.5. It doesn't go into detail but maybe with the device offline or a register issue, it froze up.
Improvements to Modbus polling Modbus polling is no longer affected by prolonged network disruptions.
(CID:131958890)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:08 AM
Dear John Smith,
I'll correct you: in fact, these fixes were made in DCE-7.4.3 😀. For example, see my answer in topic .
With respect.
(CID:131958908)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:08 AM
Thanks again! I am running 7.4.1 so, yes I need to upgrade. Thanks again for the quick reply as well!
(CID:131958914)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:43 PM . Last Modified: 2024-04-05 12:08 AM
Ok, thanks for the good feedback 😀.
(CID:131958919)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:44 PM . Last Modified: 2024-04-05 12:08 AM
It is loaded with Errors in /var/log/messages
The errors are:
Modbus_session_open: open session failed - Too many open files
nbModbusScannerCreateScan: Error creating Modbus session on
failscan:Marking scan of
Error creating scan for
nbVarLibAccessContextCreateInNS: cannot open /dev/nbVariablesFree
all the
(CID:130681811)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:44 PM . Last Modified: 2024-04-05 12:08 AM
Dear John Smith,
I would, after all, reboot the DCE-server first and watch for some time for the problem TCP/IP Modbus device.
With respect.
(CID:130681815)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:44 PM . Last Modified: 2024-04-05 12:08 AM
That seems to have fixed my issue! The whole server is working better and the device scans have been re-scanning every few minutes now!
Thanks for the help! I will keep watching it and see.
I have another issue where the device discovery is slow and shows "initializing" for a long time but I will post that in another question.
Regards,
J
(CID:130681855)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:44 PM . Last Modified: 2024-04-05 12:08 AM
Ok, thanks so much for the good feedback 😀.
(CID:130681866)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:44 PM . Last Modified: 2024-04-05 12:08 AM
So it worked but there are other issues. Does someone here know what these errors mean?
nbModbusScan: Modbus_session_open: open session failed - Too many open files
nbModbusScan: nbVarLibAccessContextCreateInNS: cannot open /dev/nbVariablesFree
(CID:131336303)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:44 PM . Last Modified: 2024-04-05 12:08 AM
Dear John Smith,
I will not prove, but the reason for the above problems can be, for example, problems with JVM, similar to those described in topic . What is your version of DCE software?
With respect.
(CID:131337115)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 04:44 PM . Last Modified: 2023-10-22 01:26 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.