Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

DCE to calculate power from current?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE to calculate power from current?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2024-04-08 11:48 PM

0 Likes
4
806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2024-04-08 11:48 PM

DCE to calculate power from current?

 

 Hi, All.

 There is a Branch Circuit power meter with intermediate functionality (SE BCPM version B), which means the device monitors a lot of options (voltage, current, power etc) for its mains and only currents for the branch circuits, which are none other than server cabinets rack pdu. 

So, it's nice to see currents for the rack PDUs, but to see power consumption would be even nicer 😀

Given that voltage could be get from mains at any given time, it's very simple to calculate an apparent power for branch circuits. 

We're able to modify particular values using ddf file with such kind of DDF code:


0.001
register3903

 

The question is if it possible to use another register as an argument for the calculation instead of a number?

Something like that:

 



register3905
register3903

Thanks

(CID:106208264)

Labels
  • Labels:
  • Data Center Expert
  • DDF
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2024-04-08 11:48 PM

0 Likes
2
806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2024-04-08 11:48 PM

Hi Nick,

 

For any DDF edits, I strongly recommend working with multivendorsupport@apc.com .  This does not seem terribly intrusive however I have seen incorrectly edited DDF files cause issues with the system up to and including failure of the system to fully boot. Additionally, if you edit a DDF and in the future that DDF is updated which does happen  from time to time (system upgrades, etc) that DDF may be overwritten and the sensor will no longer work.

 

Steve

(CID:106208284)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2024-04-08 11:48 PM

In response to DCIM_Support
0 Likes
0
806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2024-04-08 11:48 PM

Thanks for the heads up, Steve. I am aware about of all of it. I've been working with DDF for some years and succesfully created a number of it. But the quiestion was not about DDF structure but about is it possible in principle.

(CID:106208285)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2024-04-08 11:48 PM

In response to DCIM_Support
0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2024-04-08 11:48 PM

Hi Nick,

 

no I totally understood your question. Since multivendor does the DDF creation, they are also the best option for discussing what options are available for DDF creation and how that would best be achieved. 

 

Steve

(CID:106209095)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2023-10-31 10:44 PM

0 Likes
0
808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 03:59 AM . Last Modified: ‎2023-10-31 10:44 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of