DCE system upgrade

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE system upgrade
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
Ninh_NV
Ensign Ninh_NV Ensign
Ensign

Posted: ‎2025-06-15 07:51 PM

0 Likes
1
231
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-15 07:51 PM

DCE system upgrade

​Hello Expert,
 
I am working on deal for DCE upgrade project, need your advise here.
 
Currently, Customer site use DCE version 7.4.1 to monitor 100 devices.
 
They wish to upgrade to latest DCE  version to monitor:
 
  1. Existing  100 device (they expect to migrate from old DCE 7.4.1 to new DCE version)
  2. Additional 100 new device.
 
I need your help to check:
 
+ What is procedure to do this upgrade in order to minimize downtime of DCE operation.
+ For license, can we price for only 100 new device, and existing 100 device migration will not be counted for new license in order to save customer budget.
 
 
Thank you,
Ninh
Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2025-06-16 05:28 AM

2 Likes
0
217
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-16 05:28 AM

Hi @Ninh_NV ,

 

You're at a very old version and I can not recommend that you go through all the upgrades necessary to get to the current version of 8.3. You would need to upgrade incrementally all the way to 7.8.1 and we always recommend that you create backups along the way in cans there are any issues. Once you hit 7.8.1, you'll need to go through a process that's going to require that you deploy a new version for 7.9.0 (not a normal upgrade) and import the 7.8.1 backup.

 

Here's the info on how to obtain the upgrades:

https://community.se.com/t5/DCE-downloads/Complete-update-process-for-DCE/ta-p/446772

Here's info on how to upgrade to 7.9.0 and beyond):

https://community.se.com/t5/DCE-downloads/Complete-upgrade-process-for-DCE-7-9-0/ta-p/446776

 

Please also keep in mind that if you have a hardware server, you may not be able to install some newer versions. Please see this FAQ:
https://community.se.com/t5/Data-Center-Expert-release-notes/Data-Center-Expert-7-9-x-and-newer-serv...

 

In the end, I recommend going to 8.0 directly and recreating your system manually. With only 100 devices, it'll save a lot of time and effort.

 

Adding a new license is quite easy and I won't go through it here but I will say that if you need access o the portal mentioned in a previous link, you'll need to contact support directly anyway so they can assist with this too.


Thanks,

Steve

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2025-06-16 05:28 AM

2 Likes
0
218
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-06-16 05:28 AM

Hi @Ninh_NV ,

 

You're at a very old version and I can not recommend that you go through all the upgrades necessary to get to the current version of 8.3. You would need to upgrade incrementally all the way to 7.8.1 and we always recommend that you create backups along the way in cans there are any issues. Once you hit 7.8.1, you'll need to go through a process that's going to require that you deploy a new version for 7.9.0 (not a normal upgrade) and import the 7.8.1 backup.

 

Here's the info on how to obtain the upgrades:

https://community.se.com/t5/DCE-downloads/Complete-update-process-for-DCE/ta-p/446772

Here's info on how to upgrade to 7.9.0 and beyond):

https://community.se.com/t5/DCE-downloads/Complete-upgrade-process-for-DCE-7-9-0/ta-p/446776

 

Please also keep in mind that if you have a hardware server, you may not be able to install some newer versions. Please see this FAQ:
https://community.se.com/t5/Data-Center-Expert-release-notes/Data-Center-Expert-7-9-x-and-newer-serv...

 

In the end, I recommend going to 8.0 directly and recreating your system manually. With only 100 devices, it'll save a lot of time and effort.

 

Adding a new license is quite easy and I won't go through it here but I will say that if you need access o the portal mentioned in a previous link, you'll need to contact support directly anyway so they can assist with this too.


Thanks,

Steve

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore