DCE modbus communication problem

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE modbus communication problem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:14 PM . Last Modified: ‎2024-04-05 12:17 AM

0 Likes
4
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 PM . Last Modified: ‎2024-04-05 12:17 AM

DCE modbus communication problem

 Dear sir,

    Recently I met some problem with DCE System version 7.4.3, please help me.
    
    1. How the retry time in moniting modbus device works? I tried to modify the retry time,
       but looked at the journal, it seemed no effort, retry times ran out quickly.

    2. I saw many "Received error: Unknown error" in the journal, but I didn't know what happened.
       Is there some details for me? Or somewhere to find the option for details?

    3. I also saw many "Unexpected Response" in the journal, it means the length of received message
       is not equal to that expected. But after checking the content, I found it is just a malposition.
       The system actually had got the answer of last request.

    4. Is there any way to capture the modbus TCP package?

    Attachment is recently journal.
IP:122.192.1.32
250250

(CID:130092500)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:14 PM . Last Modified: ‎2024-04-05 12:17 AM

0 Likes
2
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 PM . Last Modified: ‎2024-04-05 12:17 AM

Dear guanyc,

Thank you for your logs, I looked at them and I can identify a number of common errors:

SLAVE_DEVICE_BUSY
GATEWAY_TARGET_DEVICE_FAILED_TO_RESPOND
SLAVE_DEVICE_FAILURE

Which for obvious reasons lead to the appearance of a DCE daemon scanning error:

modbus_process_timeout_cbk: read timed out for host 122.192.1.32

Therefore, it is possible to say with a high probability: considering, that you have at least 6 slaves connected on the same Modbus serial line, you have an hardware problem of a Modbus serial line.

For this reason, there are a lot of simple recommendations, for example, my answer to the post :

  1. reduce number of Modbus slave devices on one IP address (to 5-8);
  2. reduce the frequency poll of Modbus slave devices (one poll in 2-3 minutes);
  3. increase the number of attempts of poll for each of problem Modbus slave devices (not 3, and 5-6 attempts – for DCE-7.3.1 and newer);
  4. increase timeout between unsuccessful attempts poll of Modbus slave devices (for example, up to 15 seconds – for DCE-7.3.1 and newer).

As option it is possible to reduce number of sensors, which are read out on Modbus slave devices.

And at last, to try to understand, and probably to reveal and eliminate defects of the Modbus serial communication line between Modbus devices. Practically, the last recommendation can be the most effective and useful.

I hope this helps you.

If you have any questions, please ask.

With respect.

(CID:130092563)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:14 PM . Last Modified: ‎2024-04-05 12:17 AM

0 Likes
2
1957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:14 PM . Last Modified: ‎2024-04-05 12:17 AM

Dear guanyc,

Thank you for your logs, I looked at them and I can identify a number of common errors:

SLAVE_DEVICE_BUSY
GATEWAY_TARGET_DEVICE_FAILED_TO_RESPOND
SLAVE_DEVICE_FAILURE

Which for obvious reasons lead to the appearance of a DCE daemon scanning error:

modbus_process_timeout_cbk: read timed out for host 122.192.1.32

Therefore, it is possible to say with a high probability: considering, that you have at least 6 slaves connected on the same Modbus serial line, you have an hardware problem of a Modbus serial line.

For this reason, there are a lot of simple recommendations, for example, my answer to the post :

  1. reduce number of Modbus slave devices on one IP address (to 5-8);
  2. reduce the frequency poll of Modbus slave devices (one poll in 2-3 minutes);
  3. increase the number of attempts of poll for each of problem Modbus slave devices (not 3, and 5-6 attempts – for DCE-7.3.1 and newer);
  4. increase timeout between unsuccessful attempts poll of Modbus slave devices (for example, up to 15 seconds – for DCE-7.3.1 and newer).

As option it is possible to reduce number of sensors, which are read out on Modbus slave devices.

And at last, to try to understand, and probably to reveal and eliminate defects of the Modbus serial communication line between Modbus devices. Practically, the last recommendation can be the most effective and useful.

I hope this helps you.

If you have any questions, please ask.

With respect.

(CID:130092563)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:15 PM . Last Modified: ‎2024-04-05 12:17 AM

In response to DCIM_Support
0 Likes
0
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:15 PM . Last Modified: ‎2024-04-05 12:17 AM

 

Dear sir,

 

    Thank you for reply!

 

    1. I have 6 devices divided into 2 groups, one has 2 and the other has 4. The new modbus TCP gateway

 

    supports isolation(by different ports), it works properly now.

 

    2. I set the timeout to 60 seconds, but in journal it appears not as long as 60 seconds.

 

    3. Can you give some test documents or softwares for serial lines?

 

(CID:130093906)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:15 PM . Last Modified: ‎2024-04-05 12:17 AM

In response to DCIM_Support
0 Likes
0
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:15 PM . Last Modified: ‎2024-04-05 12:17 AM

Dear guanyc,

2. I set the timeout to 60 seconds, but in journal it appears not as long as 60 sec

If I understand you correctly, and this is really a connection timeout, then this is too much.

Remember: the more you have connected slaves on one same serial line, the less connection timeout should be. Otherwise, the DCE-server will wait too long for communication with only one slave device (especially when the connection is bad) and deny service to other slave devices. Practically, the communication timeout should be selected no more than 10...15 seconds with several slave devices.

To be exact, please show a screenshot from your DCE-7.4.3 where it would be nice to see the scan parameters of any your problem TCP Modbus slave device.

3. Can you give some test documents or softwares for serial lines?

I've been using the simple yet powerful utility Modpoll Modbus Master Simulator for a long time. This utility exists for different platforms, has an excellent help and is easy to use. With the help of this utility it is possible to perform a good diagnosis of your serial communication lines.

Also, do not forget, that the very first point for diagnosing your serial communication line should be directly a TCP/IP Modbus gateway. Any good TCP/IP Modbus gateway should have a statistics menu, where in an accessible form you can find out if there are any errors or problems on the serial communication line? This is a very important point, about which I wrote in detail in a similar topic , for example:

I hope this is what you need.

With respect.

(CID:130094034)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 04:15 PM . Last Modified: ‎2023-10-22 01:26 AM

0 Likes
0
1956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 04:15 PM . Last Modified: ‎2023-10-22 01:26 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of