DCE device discovery using RADIUS credentials

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

orlandogarcia
Ensign Ensign
Ensign

DCE device discovery using RADIUS credentials

Is it possible to use RADIUS credentials in the Device File transfer settings?

3 Replies 3
Valentin_Kozlov
Lieutenant Lieutenant
Lieutenant
0 Likes
2
809

Re: DCE device discovery using RADIUS credentials

Hi!

You cant use RADIUS while discovering devices, but you can specify user and password for every device or address range individually.

orlandogarcia
Ensign Ensign
Ensign
0 Likes
1
807

Re: DCE device discovery using RADIUS credentials

Hi Valentin,

 

Today I had the customer try a discovery, we entered his RADIUS credentials in the device file transfer settings and the discovery was successful.  

Valentin_Kozlov
Lieutenant Lieutenant
Lieutenant
0 Likes
0
801

Re: DCE device discovery using RADIUS credentials

Glad to hear it!

Yes, if you enter domain/RADIUS credentials in the device transfer settings and your NMC is configured properly to use RADIUS, it will work fine.

 

I mean that you can't configure DCE to use RADIUS in order to manage DCE's access to NMC based on some criteria via RADIUS service.

 

Sorry for misunderstanding.