DCE TCP Modbus module to PME communication issue

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
6
437

DCE TCP Modbus module to PME communication issue

This question was originally posted on DCIM Support by Kaloyan Georgiev on 2016-08-08


Hello,

I have installed PME 8.1 and DCE 7.3.1 with Modbus TCP module.

When I try to read some data in PME from DCE, I get an "Invalid data address" modbus error. It is not a timeout, so the communication is working.

Can you help me connecting the two softwares together?`

The information about the error is in the attached pictures.

(CID:106892092)

6 Replies 6
DCIM_Support
Picard
Picard
0 Likes
4
437

Re: DCE TCP Modbus module to PME communication issue

This answer was originally posted on DCIM Support by Law TJ on 2016-08-08


Hi, try to read with 331020 instead. Thanks

(CID:107448170)

DCIM_Support
Picard
Picard
0 Likes
0
437

Re: DCE TCP Modbus module to PME communication issue

This comment was originally posted on DCIM Support by Law TJ on 2016-08-08


Modbus TCP output only able to start from register 31000 as the option when you generate the register list "Please choose a register value between 31000 and 39999" So you may need to read as Input register, @31000, and in Modbus address, the register address will be 331000

(CID:107448172)

DCIM_Support
Picard
Picard
0 Likes
0
437

Re: DCE TCP Modbus module to PME communication issue

This comment was originally posted on DCIM Support by Stine Hansen on 2016-08-11


Hi Kaloyan Georgiev, did you try the suggestions above? Best, Stine

(CID:107448177)

DCIM_Support
Picard
Picard
0 Likes
0
437

Re: DCE TCP Modbus module to PME communication issue

This comment was originally posted on DCIM Support by Kaloyan Georgiev on 2016-08-15


Hello, I tried and I have a success. The problem was that instead of address 31020 i should use 331021. Now everything is OK. Thank you for the support! Regards, Kaloyan

(CID:107448176)

DCIM_Support
Picard
Picard
0 Likes
0
437

Re: DCE TCP Modbus module to PME communication issue

This comment was originally posted on DCIM Support by Stine Hansen on 2016-08-15


That's great news, Kaloyan Georgiev! Thanks for sharing. Regards, Stine

(CID:107448178)

DCIM_Support
Picard
Picard
0 Likes
0
437

🔒 Closed

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.