Hello,
I have installed PME 8.1 and DCE 7.3.1 with Modbus TCP module.
When I try to read some data in PME from DCE, I get an "Invalid data address" modbus error. It is not a timeout, so the communication is working.
Can you help me connecting the two softwares together?`
The information about the error is in the attached pictures.
(CID:106892092)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:53 AM . Last Modified: β2024-04-08 11:31 PM
Hi, try to read with 331020 instead. Thanks
(CID:107448170)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:53 AM . Last Modified: β2024-04-08 11:31 PM
Modbus TCP output only able to start from register 31000 as the option when you generate the register list "Please choose a register value between 31000 and 39999" So you may need to read as Input register, @31000, and in Modbus address, the register address will be 331000
(CID:107448172)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:53 AM . Last Modified: β2024-04-08 11:31 PM
Hi Kaloyan Georgiev, did you try the suggestions above? Best, Stine
(CID:107448177)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:53 AM . Last Modified: β2024-04-08 11:31 PM
Hello, I tried and I have a success. The problem was that instead of address 31020 i should use 331021. Now everything is OK. Thank you for the support! Regards, Kaloyan
(CID:107448176)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:53 AM . Last Modified: β2024-04-08 11:31 PM
That's great news, Kaloyan Georgiev! Thanks for sharing. Regards, Stine
(CID:107448178)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:53 AM . Last Modified: β2023-10-31 10:44 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.