DCE SNMPv3 communication issue

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE SNMPv3 communication issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:49 PM . Last Modified: β€Ž2024-04-08 12:25 AM

0 Likes
11
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:49 PM . Last Modified: β€Ž2024-04-08 12:25 AM

DCE SNMPv3 communication issue

We are running DCE 7.4.3 but meet this issue with previous versions

we are monitoring Emerson PDU and IBM PDU through SNMPv3

From time to time DCE loose the connection with some PDUs and the connectivity never come back to normal unless rebooting DCE (for example when the PDU card is restarted)...
and as there is no SNMP logging in DCE, it is difficult to investigate...

Any recommendation about SNMPv3 configuration? polling, timeout, number of retries, authentication and privacy types?

~ 200 Emerson and IBM PDU

We hesitate to reconfigure all our PDU with SNMPv1 even if it is less secure...

 

(CID:120131308)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

0 Likes
9
1295
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

Hi Yannick BARRAUD,

From time to time DCE loose the connection with some PDUs and the connectivity never come back to normal unless rebooting DCE (for example when the PDU card is restarted)...

I.e., the communication was restored only after rebooting the DCE-server or only after rebooting the PDU card?

and as there is no SNMP logging in DCE, it is difficult to investigate...

This is not quite true: in your case, you need to do  and then carefully examine the entries in the logfile /var/log/messages, that relate to your problematic SNMP v3 devices. For more information on this logfile see my answer in topic .

With respect.

(CID:120134267)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

In response to DCIM_Support
0 Likes
0
1296
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

In addition, in the DCE-client on the problem SNMP v3 device, did you try to do "Request Device Scan"?

(CID:120134273)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

In response to DCIM_Support
0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

Thanks for this helpul link.
I already request to see DCE log (https://dcimsupport.apc.com/questions/110008012) but I was told there is not scan log

Rebooting the PDU card has no impact, I have to reboot DCE to restore the communication.

(CID:120134296)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

In response to DCIM_Support
0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

An additional question: on the PDU card side, you looked at the corresponding logfiles or is it impossible? Maybe there you will find the answer?

With respect.

(CID:120134290)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

In response to DCIM_Support
0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

Request Device Scan has no effect on the communication issue

I checked the messages logfile but I can only see this error

Mar  8 08:26:05  nbSNMPScan: failScan: Marking scan of xxx.xxx.xxx.xxx with SCAN_FAILED resultcode.

(CID:120134298)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

In response to DCIM_Support
0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

Ok, this is the result πŸ˜€.

Tell, please, does this SNMP v3 device poll only one DCE-server or do you have multiple DCE-servers?

Or maybe you have another monitoring system that can poll your SNMP v3 devices?

(CID:120134286)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

In response to DCIM_Support
0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

Additional question: in the Device -> SNMP Device Settings -> Device Scan Settings -> Edit Device Scan Settings menu, have you tried to change the Scan Interval (minutes), Timeout (seconds) and Retries settings (increase them)?

(CID:120134281)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

In response to DCIM_Support
0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:25 AM

Thanks for your help

My colleague has finally decided to switch back all the PDU to SNMPv1...

Best Regards

(CID:120134276)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:24 AM

In response to DCIM_Support
0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:50 PM . Last Modified: β€Ž2024-04-08 12:24 AM

Additional question: in the Device -> SNMP Device Settings -> Device Scan Settings -> Edit Device Scan Settings menu, have you tried to change the Scan Interval (minutes), Timeout (seconds) and Retries settings (increase them)? = Have anyone tried this yet ?

(CID:128752690)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:51 PM . Last Modified: β€Ž2024-04-08 12:24 AM

In response to DCIM_Support
0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:51 PM . Last Modified: β€Ž2024-04-08 12:24 AM

Dear juice,

I have not tried it, because it was not necessary. Therefore, I asked you to try it πŸ˜€.

With respect.

(CID:128752715)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-03 04:51 PM . Last Modified: β€Ž2023-10-22 01:19 AM

0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-03 04:51 PM . Last Modified: β€Ž2023-10-22 01:19 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of