DCO 8.1 - Utility source as top of power path?
  • DCO 8.1 - Utility source as top of power path?
129
112
72
Posted: ‎2020-07-03 04:51 PM . Last Modified: ‎2024-04-08 12:24 AM
897
I have a customer that has some non-critical server loads on a utility feed only, no UPS.  Is it possible to model this as the top of the power path or do you still have to model a UPS to get powerpath coloring and auto cabling?  if so, is this on the roadmap for a future release?
(CID:120131436)
  • Data Center Operation
897
Hi Andrew,
Yes, currently in 8.1 it is possible to model power path without UPS. For capacity calculations, make sure that the PDU has "Input breaker" configured, example:
Kind regards
(CID:120131514)
Replies 4
898
Hi Andrew,
Kind regards
(CID:120131514)
Thanks Jef!  I thought it was added in 8.1, but couldn't find anything on specific on DCIM support about it...
(CID:120131567)
You are most welcome, Andrew
Kind regards
(CID:120131964)
Posted: ‎2020-07-03 04:51 PM . Last Modified: ‎2023-10-22 01:31 AM