Posted: β2020-07-03 04:49 PM . Last Modified: β2024-04-08 12:25 AM
We are running DCE 7.4.3 but meet this issue with previous versions
we are monitoring Emerson PDU and IBM PDU through SNMPv3
From time to time DCE loose the connection with some PDUs and the connectivity never come back to normal unless rebooting DCE (for example when the PDU card is restarted)...
and as there is no SNMP logging in DCE, it is difficult to investigate...
Any recommendation about SNMPv3 configuration? polling, timeout, number of retries, authentication and privacy types?
~ 200 Emerson and IBM PDU
We hesitate to reconfigure all our PDU with SNMPv1 even if it is less secure...
(CID:120131308)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:25 AM
Hi Yannick BARRAUD,
From time to time DCE loose the connection with some PDUs and the connectivity never come back to normal unless rebooting DCE (for example when the PDU card is restarted)...
I.e., the communication was restored only after rebooting the DCE-server or only after rebooting the PDU card?
and as there is no SNMP logging in DCE, it is difficult to investigate...
This is not quite true: in your case, you need to do and then carefully examine the entries in the logfile /var/log/messages, that relate to your problematic SNMP v3 devices. For more information on this logfile see my answer in topic .
With respect.
(CID:120134267)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:25 AM
In addition, in the DCE-client on the problem SNMP v3 device, did you try to do "Request Device Scan"?
(CID:120134273)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:25 AM
Thanks for this helpul link.
I already request to see DCE log (https://dcimsupport.apc.com/questions/110008012) but I was told there is not scan log
Rebooting the PDU card has no impact, I have to reboot DCE to restore the communication.
(CID:120134296)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:25 AM
An additional question: on the PDU card side, you looked at the corresponding logfiles or is it impossible? Maybe there you will find the answer?
With respect.
(CID:120134290)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:25 AM
Request Device Scan has no effect on the communication issue
I checked the messages logfile but I can only see this error
Mar 8 08:26:05nbSNMPScan: failScan: Marking scan of xxx.xxx.xxx.xxx with SCAN_FAILED resultcode.
(CID:120134298)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:25 AM
Ok, this is the result π.
Tell, please, does this SNMP v3 device poll only one DCE-server or do you have multiple DCE-servers?
Or maybe you have another monitoring system that can poll your SNMP v3 devices?
(CID:120134286)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:25 AM
Additional question: in the Device -> SNMP Device Settings -> Device Scan Settings -> Edit Device Scan Settings menu, have you tried to change the Scan Interval (minutes), Timeout (seconds) and Retries settings (increase them)?
(CID:120134281)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:25 AM
Thanks for your help
My colleague has finally decided to switch back all the PDU to SNMPv1...
Best Regards
(CID:120134276)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:50 PM . Last Modified: β2024-04-08 12:24 AM
Additional question: in the Device -> SNMP Device Settings -> Device Scan Settings -> Edit Device Scan Settings menu, have you tried to change the Scan Interval (minutes), Timeout (seconds) and Retries settings (increase them)? = Have anyone tried this yet ?
(CID:128752690)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:51 PM . Last Modified: β2024-04-08 12:24 AM
Dear juice,
I have not tried it, because it was not necessary. Therefore, I asked you to try it π.
With respect.
(CID:128752715)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 04:51 PM . Last Modified: β2023-10-22 01:19 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.