DCE - Event Log SNMP Trap

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE - Event Log SNMP Trap
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

0 Likes
6
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

DCE - Event Log SNMP Trap

Hi Community, Hi, emrekoca

 

My customer wants to have event logs in DCE which is who is log in or who change  threshold for information security. They are using SIEM Archsight software for controlling security logs, so they said they can give event logs only three way those are SNMP trap, Syslog or Database. Finally, please can you share me how can i send event logs with  my customer.

 

Kind Regards

Kerem

 

(CID:105465723)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

Hi Kerem,

 

This functionality does not yet exist within StruxureWare DCE. Product management is looking at such an audit trail for future releases but I have no definitive date to share, sorry. I've added this post to the enhancement request already in our system.


Steve

(CID:105465743)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

0 Likes
0
1397
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

Hi Kerem,

 

This functionality does not yet exist within StruxureWare DCE. Product management is looking at such an audit trail for future releases but I have no definitive date to share, sorry. I've added this post to the enhancement request already in our system.


Steve

(CID:105465743)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

0 Likes
3
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

Hi Kerem,

Concerning your question "...how can i send event logs with  my customer".

First, eventlog on different categories which interest you, can be looked and save in a html-format to the address http:///desktop/#eventlog .

Secondly, the same eventlog recorded on the DCE server in PostgreSQL table pg_eventlog_message, that can be much more interesting to your customer. This table can be downloaded simply from the DCE server: look, please, at this useful subject: How to download Capture logs on Data Center Expert

I am always glad to help.

(CID:105465769)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

In response to DCIM_Support
0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

Hi Spezialist, Sorry for misundestanding.. SIEM just want real time audit event log which can be cef(Syslog) or SNMP trap not download. Regards Kerem

(CID:105465792)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

In response to DCIM_Support
0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

Hi Kerem

 

Please assist.

I have downloaded the DCE event log and used winzip to extract the data, however i am not able to open it or get some sort of list of valuable data. There are various folders and txt files which im unable to understand.

Is there anyway to extract these log files into a exel spreadsheet\word doc to better understand these logs? Or is there a better way to extract logs ?

 Kind regards

 

(CID:126177444)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

In response to DCIM_Support
0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2024-04-09 01:06 AM

Dear juice,

I have downloaded the DCE event log and used winzip to extract the data, however i am not able to open it or get some sort of list of valuable data. There are various folders and txt files which im unable to understand.

You have downloaded and unpacked DCE-server system logs. I.e., these are Linux OS server log files and they have a lot of payload, especially for the purpose of diagnosing various problems. Therefore, if you are not familiar with Linux OS or are familiar at the level of a simple desktop user, then for you these files will be incomprehensible and useless. Therefore, it is recommended to send these log files to Schneider Electric employees, if you have any problems with your DCE-server.

Is there anyway to extract these log files into a exel spreadsheet\word doc to better understand these logs? Or is there a better way to extract logs ?

No, this is impossible because of the reason I wrote above.

If, however, you want to understand the structure and purpose of DCE-server system logs a little, I recommend to take a look at my answers in topic  about this. But again, without a thorough knowledge of Linux OS, you will not just be able to figure it out.

In any case, I will be happy to answer your questions 😀.

With respect.

(CID:126177453)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2023-10-31 10:26 PM

0 Likes
0
1396
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:48 PM . Last Modified: ‎2023-10-31 10:26 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore