DCE - Change from SNMPv1 to v3 in Expert

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE - Change from SNMPv1 to v3 in Expert
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

0 Likes
8
1949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

DCE - Change from SNMPv1 to v3 in Expert

Hi,

I got a nice task from our IT security to replace all SNMP communication from version 1 to version 3 on all monitored devices in StruxureWare Expert.

I have more than 600 monitored devices (mostly APC ATS/PDU/UPS) therefore I would not like to do it one by one on each equipment.

I guess "APC SNMP Device Configuration ..." will be my friend to setup on device side. But how I can modify the global SNMP scan settings to avoid outage or seemless transition in the monitoring?

Is there anyone who did the same in the past on multiple device? I just need a high level plan how to do it in a nice way.

Thanks.

(CID:126181235)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

0 Likes
6
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

Hi Mate,

 

I suggest checking out k-base FA158442. It goes through the suggested sequences and should halp out a lot.

 

Steve

(CID:126181244)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

Hi Steven,

I went thru your suggested k-base FA158442. How it is possible to do it in batch?

I created a Template in "APC SNMP Device Configuration" where I provided the SNMPv3 settings and disabled version 1.

I tried to apply to a few device but I got connectivity failure. I checked the SNMP device settings and those are still showing SNMPv1 protocol so ddi not change to v3.

(CID:128067449)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

Hi Mate,

 

If there's an issue with the file transfer, you'll want to go to the following menu:

Device–>SNMP Device Configuration settings–>Device File Transfer Settings...

Make sure the port, protocol, and user/password combinations match that of the NMCs that you're trying to configure. If not, or if they are blocked over the network, you'll not be able to push the configurations over to the devices.

 

Steve

 

(CID:128067656)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

Hi Steve,

The configuration has been successfully pushed to device because I manually checked and logged in via web. But the switchover from version 1 to 3 in DCE is not working. DCE is still want to use v1 but of course it is not working because is disabled on the device.

(CID:128067897)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:50 AM

Hi Mate,

 

The only way DCE changes that is when the configuration is pushed in the way it was done in that document. As you've likely seen, you can't edit the version of SNMP used in the communications settings  fields of DCE. 

 

The only 2 things I can suggest are to:

1: Try chqanging everything back then make sure you follow the document step by step, or

2: Delete the devices and re-add them using SNMP version 3.

 

Thanks,

Steve

(CID:128067906)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:49 AM

In response to DCIM_Support
0 Likes
0
1951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:49 AM

Thank you, I successfully changed from v1 to v3 on most of the APC devices.

 

What about non APC devices (such as Emerson/Eaton UPS)? How I can change those without losing historical data?

(CID:128748065)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:49 AM

In response to DCIM_Support
0 Likes
0
1951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2024-04-05 03:49 AM

Hi Mate,

Since we can't configure them through DCE, DCE doesn't know that the communications protocol has changed and as you've seen, you can not manually change that. You'll need to delete and re-add the device.

 

Steve

 

(CID:128748083)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2023-10-22 01:14 AM

0 Likes
0
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:26 AM . Last Modified: ‎2023-10-22 01:14 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of