We are looking into sizing the bandwidth to the DCE assuming a maximum of 4025 nodes per DCE. Does anyone has any estimates for this? The previous answers does not seem very helpful. Understandably, it is dependent on a number of factors, but can Schneider make some assumptions provide an estimate? Thank you.
(CID:126882683)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:59 AM . Last Modified: 2024-04-05 03:39 AM
Hello. In my experience the amount of bandwidth is trivial. SNMP using UDP has little impact on the network. I would be looking at
Get these two things right and you should be well placed. You may find more on the site and of course if your organisation is very pedantic you can use wireshark is similar to prove to those who need proof
cheers
(CID:126882705)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:59 AM . Last Modified: 2024-04-05 03:39 AM
Hello. In my experience the amount of bandwidth is trivial. SNMP using UDP has little impact on the network. I would be looking at
Get these two things right and you should be well placed. You may find more on the site and of course if your organisation is very pedantic you can use wireshark is similar to prove to those who need proof
cheers
(CID:126882705)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:59 AM . Last Modified: 2023-10-22 01:14 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.