Hi, I am trying to size the bandwidth required between DCO and DCE. Where DCE is integrated with DCO, DCO will pull all the power, sensor, device information data and perform full alarm syncronization etc using the default settings. What is the bandwidth required for DCO to communicate with a DCE with 4025 nodes?
(CID:126882887)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:59 AM . Last Modified: 2024-04-05 03:39 AM
Hi Lai Yuan,
The bandwidth requirements is naturally dependent on the expected amount of alarms and monitored devices.
For StruxureWare Data Center Expert it is estimated that every alarm will be around 2000 characters in size.
Sensor data has approximately the same size but is transferred more often (depending on the integration configuration).
The alarm and sensor data are bidirectional communicated with the majority of data going to DCO. Furthermore, a catch-up job, that is running on a hourly basis (configurable) this job will poll number of active alarms * 2000 chars.
Hope this helps,
Kind regards
(CID:126883041)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:59 AM . Last Modified: 2023-10-20 05:02 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.