EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 02:52 PM . Last Modified: β2024-04-03 11:45 PM
Hi,
I need to ingerate DCE 7.6 with Eco Building Operation v.2.0 and I am gonna follow the procedure in the following link https://community.se.com/t5/EcoStruxure-Building-Operation/Data-Center-Expert-with-SmartStruxure-sol... but I need to confirm the following :
1- No extra Licnese is required for DCE.
2- No extra Licnese is required for EBO.
3- Is there any updated procedure or recomentations that I should follow as the mentioned procedure describes the intergration for DCE v7.2.x and SBO v1.6.
BR,
Sameeh
(CID:137106494)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 02:52 PM . Last Modified: β2024-04-03 11:45 PM
Sameeh,
I can only answer on the DCE portion.
1- No extra License is required for DCE.
Yes, there is no licenses required to enable EWS in DCE
The SBO/EBO portion, do post to the exchange community to get confirmation whether license is required for SBO/EBO to consume EWS as well as for the upgrade steps & requirements.
(CID:137106534)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 02:52 PM . Last Modified: β2024-04-03 11:45 PM
Sameeh,
I can only answer on the DCE portion.
1- No extra License is required for DCE.
Yes, there is no licenses required to enable EWS in DCE
The SBO/EBO portion, do post to the exchange community to get confirmation whether license is required for SBO/EBO to consume EWS as well as for the upgrade steps & requirements.
(CID:137106534)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 02:52 PM . Last Modified: β2024-04-03 11:45 PM
Hi Chris,
Thanks for your relpy.
BR,
Sameeh
(CID:137106783)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 02:52 PM . Last Modified: β2024-04-03 11:44 PM
You can integrato with the EWS, follw the instructions:
1 Create a User and password in the DCE
2. Create a new EWS interface in the SBO
3. In EWS serve add the DCE IP Address, Copy: DataExchange/DataExchangeService in the path an d use the user and password create an the step 1
(CID:137727789)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 02:52 PM . Last Modified: β2024-04-03 11:44 PM
Thank you very much for your reply
(CID:137728111)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 02:52 PM . Last Modified: β2023-10-22 01:13 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.