DCE 7.3.1 multiple devices have lost communication alarm

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE 7.3.1 multiple devices have lost communication alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2024-04-05 12:31 AM

0 Likes
3
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2024-04-05 12:31 AM

DCE 7.3.1 multiple devices have lost communication alarm

Good afternoon all,

we continue to be experiencing an issue where our Virtual DCE 7.3.1 generates a multitude  of communication lost alarms across multiple device types.

It seems that the lost connectivity alarms are mostly generated during the late evening or overnight hours, with hardly any occurring during business hours.

I was told it is possibly a latency issue given the server is located in one city and the the devices are spread out as far as other cities 350 Kilometers away that could be causing these timeouts. 

I checked the KBase, to see if anyone had added similar topic, recently and noticed:  . My issue is essentially the same except on version 7.3.1... using SNMPv1 and although some devices have up to date firmware the lost connectivity still occurs on them also.

Any assistance, guidance or suggestions with this issue would be greatly appreciated in the meantime I will a closer look at the above example and see if I have missed any of the steps that were offered above.

 Thank you in advance, 


Mark




(CID:129409954)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2024-04-05 12:31 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2024-04-05 12:31 AM

Hi Mark,

Intermittent SNMP issues can be difficult to pin down but if it's happening at certain times a day, that may make it easier. First, take a look at the following k-base:

http://www.apc.com/us/en/faqs/FA226273/

That goes through some basics of troubleshooting SNMP. If you think it is a latency issue, things like timeouts and retries should potentially be increased as noted in the document.

You may also want to take a look a the logs on the devices themselves. Are there other systems polling the devices at that time? Perhaps another NMS trying numerous community names if SNMP V1? The newest firmware on APC devices should be able to indicate if there is such an issue by showing unauthorized attempts. 

You may also want to look at other network activities at this time. Is there a great deal more traffic due to backups and vulnerability sweeps?

You may also want to consider getting DCE up to date. We're up to 7.5 now and there have been updates to things like SNMP processes. The issues noted in the post you mentioned would not likely be the same as SNMP version 1 and version 3 issues are different and that was version 3 specific. Still, it's best to be up to date on all aspects.

If these issues are happening at a certain time, you can also look at things on the DCE server that may be set to happen overnight such as backups being performed, discoveries set to run, etc. If the issues are happening to specific locations however, it's more likely that it is network based than server based.

 

Steve

 

(CID:129412223)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2024-04-05 12:31 AM

0 Likes
0
989
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2024-04-05 12:31 AM

Hi Mark , thanks for posting. Let's hope you find your answer here. 

Kind regards Ditte

(CID:129412062)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2024-04-05 12:31 AM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2024-04-05 12:31 AM

Hi Mark,

Intermittent SNMP issues can be difficult to pin down but if it's happening at certain times a day, that may make it easier. First, take a look at the following k-base:

http://www.apc.com/us/en/faqs/FA226273/

That goes through some basics of troubleshooting SNMP. If you think it is a latency issue, things like timeouts and retries should potentially be increased as noted in the document.

You may also want to take a look a the logs on the devices themselves. Are there other systems polling the devices at that time? Perhaps another NMS trying numerous community names if SNMP V1? The newest firmware on APC devices should be able to indicate if there is such an issue by showing unauthorized attempts. 

You may also want to look at other network activities at this time. Is there a great deal more traffic due to backups and vulnerability sweeps?

You may also want to consider getting DCE up to date. We're up to 7.5 now and there have been updates to things like SNMP processes. The issues noted in the post you mentioned would not likely be the same as SNMP version 1 and version 3 issues are different and that was version 3 specific. Still, it's best to be up to date on all aspects.

If these issues are happening at a certain time, you can also look at things on the DCE server that may be set to happen overnight such as backups being performed, discoveries set to run, etc. If the issues are happening to specific locations however, it's more likely that it is network based than server based.

 

Steve

 

(CID:129412223)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2023-10-22 01:10 AM

0 Likes
0
990
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:35 PM . Last Modified: ‎2023-10-22 01:10 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of