Connecting the DCE to BMS ? Guidelines?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Connecting the DCE to BMS ? Guidelines?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:01 AM

0 Likes
12
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:01 AM

Connecting the DCE to BMS ? Guidelines?

How to connect the DCE to BMS ? Do you have any document guide line ?

(CID:96043673)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:01 AM

0 Likes
1
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:01 AM

Hi Minh,

There is a way of adding DCE to Schneider Electric SBO through EcoStruxure Web Services. The documentation can be found at:

https://buildingsdownloads.schneider-electric.com/search#documentDetails/1383377/IT%20Infrastructure...

(CID:96043677)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:01 AM

In response to DCIM_Support
0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:01 AM

Thanks Aniruddha, however I could not download the PDF file, I have sent email request to admin for permission. Will try again later.

However, on the APPLICATION NOTE #156, I did found a StruxureWare Data Center Expert v7.2.0 Building Management System Integration doc which said:"  StruxureWare Data Center Expert is connected to the BMS through a RJ-45 port (GB1) located on the server appliance... StruxureWare Data Center Expert then becomes the gateway for all information the BMS would request." That will created a big problem to us by changing the entire building sensors connecting to DCE first then BMS. Not looking to that solution. 

I will discuss to our local APC/Schneider support

Thanks,

Minh

(CID:96043697)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:01 AM

0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:01 AM

Hi Minh,

The idea behind this integration is to converge the White space infrastructure with Building Management. You won't need to necessarily switch your sensors from BMS(typically those related to the Building) to DCE, instead you will take additional inputs from DCE from it's sensors. Also, the procedure you mentioned above is different & requires StruxureWare Data Center Expert Modbu0s TCP Output Module to export device register map for the BMS system. Additional Information can be found: at: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP95MODBUS

(CID:96043681)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:00 AM

0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:00 AM

Hi Aniruddha,

Thanks for quick respond. As under DCE there are module Building Management Setting which required a License key which is fine to me, however before purchasing a license I would like to know how DCE can talk or pull out data from BMS which is Johnson Metasys using N2 Johnsons comms protocol? Any specific hardware to convert N2 to Modbus TCP? any recommendation? 

Thanks,

Minh

(CID:96043683)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:00 AM

0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:00 PM . Last Modified: ‎2024-04-10 12:00 AM

Hi Minh,

DCE does not pull any data from the BMS. It will act as a gateway to give away all the information about it's child devices to the BMS.  The StruxureWare Data Center Expert Modbus TCP Output Module integrates data and select events from devices managed by StruxureWare Data Center Expert into an existing Building Management Systems through ethernet transmission.

(CID:96043685)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

0 Likes
1
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

HI Aniruddha,

So this case is opposite what our requirement. As currently, we have a sharing generator connected to Property Facilities BMS, and want to pull data from their BMS to our DCE.

Thanks for your assistant.

Minh

(CID:96043687)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

In response to DCIM_Support
0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

You can ask a local Technical Support to try out a Multimaster Modbus TCP Gateway, such as EGX100 to achieve this connectivity. Here you can start monitoring the Generator directly on DCE without having to integrate the BMS.

(CID:96043689)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

Hi Aniriddha,

I dont have permissions to download this document. can you give another link to download this document. I need to share the values of my UPS and Inrow units from DCE to Struxureware Enterprise server.

(CID:96043700)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

0 Likes
2
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

Hi Shaf, quoting Aniruddha's comment, the best way to monitor DCE into SBO is using DCE Modbus TCP Output. Here's the link to DCIM support:

Building Management Settings (System menu) 

 The StruxureWare Data Center Expert Modbus TCP Output Module integrates data and select events from devices managed by StruxureWare Data Center Expert into an existing Building Management Systems through ethernet transmission.

(CID:96043703)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

In response to DCIM_Support
0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

Why wouldn't EcoStruxure Web Services (EWS) be a better way to integrate DCE into SBO? You shouldn't need an additional license to pull data from DCE into SBO. Can you please clarify why the Modbus TCP Output Module is better then EWS?

(CID:96043715)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

In response to DCIM_Support
0 Likes
0
1537
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2024-04-10 12:00 AM

You are right, EWS is another option. Number of devices and data points, data transfer frequency, purpose of data (alarms? real time monitoring) etc are some factors to be considered when deciding on data interface method.

(CID:96043717)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2023-10-31 10:21 PM

0 Likes
0
1536
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 12:01 PM . Last Modified: ‎2023-10-31 10:21 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of