EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:12 PM . Last Modified: β2024-04-05 12:18 AM
Hi ,
Need a support to change mass SNMPv1 community string from public to new name . Can any one please provide me how do we do this and what will be the impact do i have to change this name on DCE as well ?
(CID:130092054)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:12 PM . Last Modified: β2024-04-05 12:18 AM
Dear Shaik Mahboob Ali,
Of course, this can be done using DCE software. Step by step how to do it I described in the recent topic . The only difference is only in the choice of parameters for editing, for example as it is shown in my screenshot:
Try it, it should work for you.
With respect.
(CID:130092130)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:12 PM . Last Modified: β2024-04-05 12:18 AM
Dear Shaik Mahboob Ali,
Of course, this can be done using DCE software. Step by step how to do it I described in the recent topic . The only difference is only in the choice of parameters for editing, for example as it is shown in my screenshot:
Try it, it should work for you.
With respect.
(CID:130092130)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:12 PM . Last Modified: β2024-04-05 12:18 AM
(CID:130092157)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:12 PM . Last Modified: β2024-04-05 12:18 AM
Ok, thanks for the feedback π.
(CID:130092163)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:12 PM . Last Modified: β2024-04-05 12:18 AM
Hi ,
I am getting communication lost and cannot see any values on web and displayed as devices unplugged but i can access the device. What could be the issue ?
(CID:130092246)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:12 PM . Last Modified: β2024-04-05 12:17 AM
updated below picture from one of the device failed to contact with server.
(CID:130092251)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:12 PM . Last Modified: β2024-04-05 12:17 AM
Dear Shaik Mahboob Ali,
I am getting communication lost and cannot see any values on web and displayed as devices unplugged but i can access the device. What could be the issue ?
1. Have you changed the public community string to your own secret string on the DCE-server as I explained it in your topic ?
2. Next, you changed the public community string to your own secret string (similar to the item 1) on your device, as I explained in this topic in the screenshot above?
updated below picture from one of the device failed to contact with server.
From what device is this screenshot? Can you show it where you could see the description of the error or problem?
In addition, usually SNMP devices do not initiates a communication with the DCE-server, but on the contrary: the DCE server initiates a communication session using the SNMP protocol with the device. Therefore, the problem with communication can be seen on the DCE-server, but not on the device as you explain it.
With respect.
(CID:130092264)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:13 PM . Last Modified: β2024-04-05 12:17 AM
Thanks i missed to change the community string from SNMPv1 settings from pic below location as well.
(CID:130092441)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:13 PM . Last Modified: β2024-04-05 12:17 AM
Congratulations, you have succeeded π.
(CID:130092476)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:13 PM . Last Modified: β2024-04-05 12:17 AM
Don't forget to change the DCE's SNMP scan settings' SNMP v1 Read community name afterwards
Device Scan Settings option 8052735a
(CID:130092140)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:13 PM . Last Modified: β2024-04-05 12:17 AM
That's right, since I wrote in response to topic .
(CID:130092146)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 04:13 PM . Last Modified: β2023-10-20 05:08 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.