EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:55 PM . Last Modified: β2024-04-08 01:08 AM
I have a PM5300 with ethernet card and I want to use it as a ethernet gateway for an only Modbus PM710.
Is that possible? Do I need any further hardware?
(CID:116364622)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:55 PM . Last Modified: β2024-04-08 01:08 AM
Dear Enric,
As far as I know, I do not think you can use PM5300 as an ethernet gateway to convert other Modbus Over RS485 to Modbus Over TCP device.
You can use the EGX100 or EGX300 to convert the Modbus RS 485 to Modbus Over TCP in order to integrate with the DCE software.
You may also want to consider Schneider Electric's Automation Server to convert the Modbus RS485 to Modbus Over TCP to integrate with DCE software.
I request you to discuss with your local country sales or tech support to know the available options.
Regards.
Bala
(CID:116364709)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:55 PM . Last Modified: β2024-04-08 01:08 AM
Dear Enric,
As far as I know, I do not think you can use PM5300 as an ethernet gateway to convert other Modbus Over RS485 to Modbus Over TCP device.
You can use the EGX100 or EGX300 to convert the Modbus RS 485 to Modbus Over TCP in order to integrate with the DCE software.
You may also want to consider Schneider Electric's Automation Server to convert the Modbus RS485 to Modbus Over TCP to integrate with DCE software.
I request you to discuss with your local country sales or tech support to know the available options.
Regards.
Bala
(CID:116364709)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 02:56 PM . Last Modified: β2023-10-20 05:04 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.