Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Success Stories Corner
  • companyImpact

Big issues in DCO?

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Big issues in DCO?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Jef
Captain Jef Captain
76
APC_Steve
Commander APC_Steve Commander
54
gsterling
Commander gsterling Commander
49
Cory_McDonald
Lt. Commander Cory_McDonald Lt. Commander
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:38 PM

0 Likes
9
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:38 PM

Big issues in DCO?

This question was originally posted on DCIM Support by Boris Majdandzic on 2018-08-13


Hello,

I have DCO Capacity 20 rack licence.

  1.  I don`t have sensor mapping options in DCO. My sensors are not shown in DCO, I have associated PDU with racks, but no option when I use right click.
  2. I have used several types of INROW genomes, but I always get recommendation to put in perforated floor tiles even though I am using HOT isle
  3. I have WIB as SNMP communication with Stulz C7000 AC units, so how can I associate this with 4 devices?

I need these answers ASAP.

Thanks in advance

 

(CID:133370719)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply
Share
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

0 Likes
6
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This answer was originally posted on DCIM Support by Jef Faridi on 2018-08-14


Hi Boris,

1- In Planning Device Association mode, after you have associated a device to your PDU, right-click on the device/PDU and select the "Sensor Mapping" from the menu.

For more details, please see the following page: Configuring branch circuit monitoring

2- Apparently you might have some down-flow CRAC(s) in your setup. Down-flow CRACs in general would require modeling/adding some perforated tiles and configured Raised floor ( right-click on the floor > Properties > Floor).

3- If I understand correctly you want to associate one DCE device to 4 models in DCO, right? if yes, then that is not supported, in DCO we can/may associate one DCE device to one model in DCO.

Kind regards

(CID:133370982)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

In response to DCIM_Support
0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This comment was originally posted on DCIM Support by spezialist on 2018-08-14


Dear Boris Majdandzic,

3- If I understand correctly you want to associate one DCE device to 4 models in DCO, right? if yes, then that is not supported, in DCO we can/may associate one DCE device to one model in DCO.

Unfortunately my doubts, which I described to you in response to the topic of , were confirmed:

If you decide to use the DCO & DCE system for the project, you should first consult the Schneider Electric staff.

Since you decided to use one WIB8000 device (SNMP) for four cooling units, you should be aware that in DCE software all four cooling units will be represented as single common SNMP device. In the future, this can cause some difficulties of a human nature when handling emergency alerts from cooling units. In addition, for the correct mapping of the temperature/humidity sensors of this single common SNMP device, some skills and knowledge will be required to be divided into four separate cooling units in the DCO software. This is also an important point, which is often ignored.

With respect.

(CID:133370989)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

In response to DCIM_Support
0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-08-14


Hello,

  1.  Problem with option"sensor" mapping was resolved with reinstalling the system. The similar issue happend on training when the 2 of us in the class didn`t have all the options in DCO.

  2. I don`t have downflow CRAC, but problem could be with the design that I have attached. I can`t find roof mounted AC units for the electrical room, or should I remove the electrical rooms for them selves? (Customer want`s to have visible all rooms in same view)

  1. Since the separation wasn`t shown in tutorial or training I will need some help with this. Can you send me any papers for this?

(CID:133371014)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

In response to DCIM_Support
0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This comment was originally posted on DCIM Support by Jef Faridi on 2018-08-14


Hi Boris,

Most likely related to the modeled cooling units. Which cooling units (from Genome Library) have you used?

Kind regards

(CID:133371029)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

In response to DCIM_Support
0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-08-14


I have used Generic InRow, Tried With Stulz Inrow & APC INrow genoms, always recommends perforated tiles.

I have already posted this in another question, but there was no answer

(CID:133371046)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

In response to DCIM_Support
0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This comment was originally posted on DCIM Support by Jef Faridi on 2018-08-14


Hi Boris,

Apparently Stulz units seem to be downflow/upflow A/C units. However issue appears to be reproducible by using the Generic InRow items (from Genome Library) - I will register a bug report for this.

Workaround:

Please try the following workaround to replace your modeled cooling units:

In Genomes right-click on your Generic InRow item > Properties > General, and then change the Manufacturer to APC:

Now add/drag this device to your floor, and then right-click > Properties > General, enter your Manufacture name (such as Stulz):

Kind regards

(CID:133371094)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

In response to DCIM_Support
0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This comment was originally posted on DCIM Support by Boris Majdandzic on 2018-08-23


Hi,

Is there example how to associate sensor to different equipment than it is associated device?

(CID:133375047)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This answer was originally posted on DCIM Support by Christian Riis on 2018-08-14


 

... should I remove the electrical rooms for them selves? (Customer want`s to have visible all rooms in same view)

The recommended approach to achieve this is to use the Floor Plan. On a Floor Plan you can arrange multiple rooms relatively to each other.

Move (or create) your rooms under the Floor Plan:

When the room editor is unlocked, you can move the rooms on the floor plan:

If you double-click the rooms they will open up in the room editor.

You can also add a background image to a Floor Plan.

(CID:133371190)

Reply
Share
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:39 PM

0 Likes
0
378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
Share

Posted: ‎2020-07-04 09:39 PM

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Share
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account?Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc